R
JPL941
What size boiler?0
Help
Your piping isn’t the worst, however the 2” size is going to create a higher steam velocity and that creates wet steam.
DL Mechanical LLC Heating, Cooling 732-882-2267 Specializing in Steam Heating
I have the same model boiler, but one size smaller. Since it's power vented, the second 2" tapping isn't available because the fan assembly covers it, so you're stuck with a single 2" tapping from the boiler.
I had my installer use a 3" header to compensate. I also raised the header about 10" higher than the recommended header height from the waterline because I had the room.
Since your main take-offs are so low, you might consider doing a drop header.
I also found that my boiler is VERY sensitive to oil and sediment in the boiler water. I had to skim it frequently for a total of something like 15 times the first year to tame it. After that it ran smoothly.
Burnham IN5PVNI Boiler, Single Pipe with 290 EDR
18 Ounce per Square Inch Gauge
Time Delay Relay in Series with Thermostat
Operating Pressure 0.3-0.5 Ounce per Square Inch0