CI Radiators, converting iron pipe to pex
vincyking11212
Member Posts: 7
Hi, I’m trying to do steam to hydronic (hot water) conversion and need some advice before installing next month. I bought a 7 section manifold to feed 6 CI radiators and 1 hot water heat blower, a navien NHB-55 (Mod con boiler), and running Homeruns 1/2 inch pex al pex. However I am concerned about my design. I am converting the entire house from a 140k BTU steam heat system with DHW to 2-Navien mod/con with single zone use. My house heat loss is 20k and the radiators will output collectively 29,700 btus and all of the runs are about 45 feet long. Also, I'm installing one boiler per unit, it is a duplex house. Any suggestions?
0
Comments
-
I think you're wasting your money. You might gain 2-3% efficiency, and the Navien won't last anywhere near as long as a cast-iron boiler. And some types of radiators won't work with hot-water.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Keep the steam, if you haven't already demolished it.
First, it will be less expensive.
Second, it will be a lot less work.
Third, it will heat better. Particularly, in that regard, have you determined whether the steam radiators -- which may or may not work for hot water -- will produce enough heat? At best you can expect only half to maybe two thirds as much heat from a given radiator on hot water as you got from steam.
Forth, have you evaluated what size boiler or boilers you really need? Steam is sized on the basis of the installed radiation ("EDR"). Hot water is sized on the basis of the heat loss of the structure.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
I already wrecked out the steam and oil tanks. I brought CI rads. What are the usually issues with using CI rads with a hydronic setup?0
-
If the sections of a radiator are only connected across the bottom, rather than at both top and bottom, water cannot circulate through them.
You would have done much better to consult with us before tearing everything out.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Its not too late for me to make the adjustments, I haven't installed the new rads yet. Do you think it is better to install the supply on the top radiator connection and the return on the bottom radiator connection (left to right)0
-
Take some pics of the rads you have and post them here.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
-
> @vincyking11212 said:
> Hi, I’m trying to do steam to hydronic (hot water) conversion and need some advice before installing next month. I bought a 7 section manifold to feed 6 CI radiators and 1 hot water heat blower, a navien NHB-55 (Mod con boiler), and running Homeruns 1/2 inch pex al pex. However I am concerned about my design. I am converting the entire house from a 140k BTU steam heat system with DHW to 2-Navien mod/con with single zone use. My house heat loss is 50k and the radiators will output collectively 29,700 btus and all of the runs are about 45 feet long. Also, I'm installing one boiler per unit, it is a duplex house. Any suggestions?
Your heatloss is 50k and radiator output is 29k??0 -
@STEAM DOCTOR that was a typo, the approx. heat loss is 20k. The house is attached and insulated.0
-
Also, it is a small building that is apporximately 1000 sq ft.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements