Grundfos Circulator
Docfletcher
Member Posts: 487
My indirect water heater circuit is making more noise than ever. The (UP 15-42 FR) circulator is currently mounted horizontally, 3/4" flange in and 1 " out. I want to change the circulator position to vertical hoping the noise will go away.
The noise I believe is directly related to water flow. Shutting the ball valve abruptly and immediately opening it once or twice causes the noise to go away compleatly for a minute or two. Then noise returns. Could the 3/4" flange in and 1 " out be causing the noise? If so, I could order a flange kit to make both in and out the same and try that before going through the trouble of remounting the circ to vertical. Thanks for your help.
The noise I believe is directly related to water flow. Shutting the ball valve abruptly and immediately opening it once or twice causes the noise to go away compleatly for a minute or two. Then noise returns. Could the 3/4" flange in and 1 " out be causing the noise? If so, I could order a flange kit to make both in and out the same and try that before going through the trouble of remounting the circ to vertical. Thanks for your help.
0
Comments
-
-
No air separator like a spirovent JR. If I mount the circ vertical it most likely would prevent air from getting trapped. The circuit does have a spirotop vent, but it installed was just to remove bulk air when water was added to the circuit at startup of the new indirect.
.0 -
-
Thanks, I get it. So the 3/4" pipe in and in and 1" out should not matter once I make for longer pipe lenghths?0
-
Are you "Pumping Away" from your expansion tank?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Not 100% sure. Older system so probably not. Tank is mounted at the system return and the circ is currently on the system supply very close to the boiler. Before the indirect was changed the circ was vertical and there was no noise. So I think I need to return it to vertical.0
-
Is the circulator motor itself horizontal. If the circulator motor is mounted vertically, motor facing down, never. Motor facing up, system pressure must be set to min. 20 psi.
What is the system pressure?0 -
18 psi @ 105F Which seems a bit high to me considering the auto fill is set at 14psi.0
-
I'm not clear on what you mean by vertical? the piping run, or motor orinatation?
They will actually run in ANY position, but they are happiest as indicated.
Noise is usually air related, unless it is a squeal from a damaged bushing.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I'm speaking of changing the circulator position and it's piping to vertical. Currently the circulator and piping are horizontal. The motor is also horizontal.0
-
A vertical piping arrangement is not going to make any more or less noise than a horizontal piping arrangement. Odds are you are trapping air somehow, and you need to take care of the air infiltration issue before you worry about moving the circ. Is the Spirovent still in place? First you say there isn't one but in the next breath say there was one installed- which is it? The pipe sizes will not play a role in the noise either, and unless there is a street 90 in the inlet side flange I find cavitation hard to believe also. My money is on air bubbles1
-
Increase the pressure to 25 psi with the pump running which reduces the size of the air bubbles and makes them easier to move around.
If that doesn't work, add some dishwashing detergent to reduce surface tension which will do the same thing.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1 -
Yeah my bad... I should have said a Spirotop vent, just to let air out while filling the indirect.
Circ has been removed/installed 3 times and noise remains. There are 1" unions at the in and out of the indirect, I will check them 1st and move on from there.
I did run at elevated PSI last year but it did not help. I guess I may try Alan's dish soap. Thanks guys...0 -
If circulator has internal flow check, then most probable it causes the noise. Try to replace it or remove.Gennady Tsakh
Absolute Mechanical Co. Inc.1 -
No flow checks in circ... Thanks0
-
I have found a tiny leak on the low pressure boiler side of the pressure regulator. Looks like it has been leaking for quite a while. .0
-
Thanks everyone for all the assistance with my noise issue. GroundUp gets kudos and abig fat Cigar for his air infiltration call which looks to be a good call. I fixed the well concealed leak and the noise problem is gone.0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements