Bypass between supply and return headers / manifolds?
woobagooba
Member Posts: 186
in Gas Heating
I've got a 3/4" copper connection between my supply and return labeled "bypass". It includes a ball valve with the handle at 45 (versus the direction of flow). Hoping someone can explain its purpose. Thanks
0
Comments
-
got a pic? Some manifolds have pressure bypass valves added on or built in. Sounds like the valve you have is a way to isolate the branches.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Here is a pic of the return manifold (supply "manifold is tangle of CI and copper in the ceiling). The bypass valve in question is on the far left end of the return manifold.
0 -
It's the cheap and horrible way to do boiler protection.
There was an error rendering this rich post.
0 -
Please explain0
-
what type of boiler?
Why a bucket under the BFD vent pipe?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Its me again
https://forum.heatinghelp.com/discussion/170834/buderus-gb142-multiple-corrosion-issues#latest
Pay no attention to the bucket. That was wanna-be-HVAC-guy draining the failing ST120 to pull what I expect to see is a decimated anode.0 -
Looks like a modcon? Nothing to protect.Steve Minnich0
-
It's a Buderus GB-142.
If its piped directly back to the return without anything else inline, shut off the valve, remove the handle and zip tie it near the valve. A bypass is counter productive on a mod con.
And whether it was supposed to be a boiler bypass or system bypass, its piped wrong either way.1 -
@HVACNUT Roger that and thank you0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements