Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Header and equalizer

retep
retep Member Posts: 13
Drop header pictures seem to show sub stantial slope how much is necessary also can I take two inch equalizer All the way back to boiler and connect Hartford with two by one and one half by two reducing t

Comments

  • Ron Jr._3
    Ron Jr._3 Member Posts: 605
    I slope mine to a bare minimum. I like the look of straight pipes lol. I think just enough pitch to make sure no condensate lays in the horizontal should be fine. And piping the equalizer full size all the way to the return is the best way to go.
  • Steamhead
    Steamhead Member Posts: 17,312
    Ron Jr._3 said:

    I slope mine to a bare minimum. I like the look of straight pipes lol. I think just enough pitch to make sure no condensate lays in the horizontal should be fine. And piping the equalizer full size all the way to the return is the best way to go.

    This.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Ron Jr._3
  • gerry gill
    gerry gill Member Posts: 3,078
    As long as the bubble breaks level in the vial, you should be all set. Alot of our drop headers set their own pitch (visibly) because we take the next larger size nipple for the downstream riser drop to header. If that makes any sense.
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

    HVACNUTRon Jr._3