400000 btu pool heater has flow
MarkMill
MarkMill Member Posts: 1
edited August 2019 in Domestic Hot Water
I was given a 400000 btu pool heater and replaced gas valve, control board, igniter. I ran 1.25 pipe for 50' then down to an existing .75 pipe for another 25' to the heater. Via manometer the static pressure is 7.8, however manifold pressure will not go above .5 ". My meter is a 275 CHF. I was wondering if the new gas valve was bad, but now think the meter is insufficient. The previiis heater was 260000 btu and ran ok until it died.
Thank you for any help.
  • Zman
    Zman Member Posts: 7,614
    edited August 2019
    Your meter is too small for 400K. Your gas pipe is undersized.
    This would be a good job for a pro...
    Albert Einstein
  • JohnNY
    JohnNY Member Posts: 3,392
    Yeah. Pipe's too small and you don't have 400,000 BTUs available anyway.
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    HVACNUT Member Posts: 7,526
    The 275 meter is spec'd for, wait for it... 275,000 BTU's.
    EBEBRATT-Ed Member Posts: 20,478
    meter too small, pipe too small. should be 1 1/2" right up to unit
    hot_rod Member Posts: 27,841
    edited August 2019
    got enough pocketbook to feed that beast, if you do get it connected? :)
    I consider pool heaters as my mother put it when we left doors open, " I'm not paying to heat the great outdoors"
  • ChrisJ
    ChrisJ Member Posts: 17,519
    edited August 2019
    To be fair he probably didn't know 275 cubic feet per hour equals roughly 275,000 btu/h.
    Before anyone says it.
    Yes, also to be fair he shouldn't be running gas piping and hooking up appliances if he doesn't know what he's doing either.
  • Zman
    Unless you are at 10,000 feet with 713 btu/cf,then it is 196,075 :)
    I was not comfortable giving specific advise and having him blow his silly self up.
    Albert Einstein
  • JUGHNE
    JUGHNE Member Posts: 11,603
    You could possibly change to a 2 PSI system.
    NOT a DIY job.
    Might cost you 1-2 months of gas though.
    The better things in life cost money. :)