Wiring Taco zone valves and circs
BillAllen
Member Posts: 103
I have 5 zones of HW. 2 zones have zone valves the other 3 zones are circs. The ZVC control board will only connect zone valves and the one circ used in connection to the ZV's. The other 3 zones looks like I need a separate SR-4 for the circs.
I was wondering how I could wire this using one board. Does the Taco make a board that incorporates Zone valves and circs together without having to buy 2 control boards?
I was wondering how I could wire this using one board. Does the Taco make a board that incorporates Zone valves and circs together without having to buy 2 control boards?
0
Comments
-
Good question, but none that I know of including other brands.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
The SR506 will work. Use one zone for the zone valves. End switches to RW on the zone board.0
-
Is there a separate pump for the zone valves?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Yes separate pump that carries 2 ZV. I have a ZVC on my truck but now it looks like I need to buy an SR506 too! Unless I'm missing something.0
-
Taco said I could do it with a SR506.0
-
-
-
Feeling invisible?HVACNUT said:Tap tap. Is this thing on?
Actually sometimes I'm the first to reply to a question, then when I come back to the thread I notice I’m about 4th and the timestamp is incorrect. Maybe your response wasn’t up when the others responded.
There was an error rendering this rich post.
1 -
Maybe0
-
if your applications is for 3 zones with circulators, and 1 zone with two zone valves and corresponding circulator, you can use the SR504-4, or if you want to have extra capacity for future use, the sr506 would work great.
follow typical wiring instructions for circulators on zones 1 through 3, and wire the zone valves to an external 24v, 40VA transformer to power 2 valves following typical wiring instructions found in ZV instruction sheet. Parallel terminals 2, and 3 on valves so when either valves have a demand from thermostat the valve end switches wired to zone 4 R&W on SR504/506 will energize corresponding pump, and fire boiler.
Hopefully this was helpful. that's the cleanest approach, easy to dianose if there is any issues, and least expensive option using one control, and a 40VA external transformer for the valves.
Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions1 -
Thanks Joe. The 2 zone valves are in another room in the ceiling where there is wiring and a transformer there. Form all the speghetti low voltage wiring there the end switches do come all the way back to where the new boiler will be that I am installing. So I assume that these 2 end switches carry both ZV's thus connect these 2 wires to 1 and 2 on the Sr506?? Is that correct?0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements