Just got the results back from Rhomar for the water in my new boiler. Note that a Adey MC3 cleaner was in the old system for a few weeks before the install, then it was thoroughly flushed, then re-filled, then de-mineralized, then MC1 inhibitor was added. The system is old converted gravity in the early 80s. Two of three zones are CI rads, one zone all baseboard with copper piping. The old steel risers to main and 2nd floors are still there; 3/4" inch copper piping connects all the risers down in the basement in series--each floor separately.
See attached test results. PH of 7.01 is neutral--should be higher, less acidic. The level of inhibitors is way too low; the chemist believes that the inhibitors may have 'complexed' --joined--with the dissolved iron and sediments in solution rendering the inhibitors ineffective. The recommendation is to drain out and re-fill this water. I told him for the time being our intention is to add a Caleffi dirtmag filter to the common return (the existing Magnaclean only filters the heating return) and add some more MC1 as if there currently none in the system. Then wait until heating season and re-test. He agreed that would be ok.
What I have to find out from Adey is if MC1+ pushes towards acidity; if so perhaps another inhibitor should be used. The sample was taken from the bottom of the Turbomax tank--after a dhw cycle so the turbulence made the debris a bit less concentrated--but it's possible the sample was not truly representative of an average, but still in the ballpark. I wonder what the results would have been in the old system--I'm thinking sometimes all these cleaners etc stir up a lot of the old rust and corrosion. I'm all ears for anyone's opinions on this.
See attached test results. PH of 7.01 is neutral--should be higher, less acidic. The level of inhibitors is way too low; the chemist believes that the inhibitors may have 'complexed' --joined--with the dissolved iron and sediments in solution rendering the inhibitors ineffective. The recommendation is to drain out and re-fill this water. I told him for the time being our intention is to add a Caleffi dirtmag filter to the common return (the existing Magnaclean only filters the heating return) and add some more MC1 as if there currently none in the system. Then wait until heating season and re-test. He agreed that would be ok.
What I have to find out from Adey is if MC1+ pushes towards acidity; if so perhaps another inhibitor should be used. The sample was taken from the bottom of the Turbomax tank--after a dhw cycle so the turbulence made the debris a bit less concentrated--but it's possible the sample was not truly representative of an average, but still in the ballpark. I wonder what the results would have been in the old system--I'm thinking sometimes all these cleaners etc stir up a lot of the old rust and corrosion. I'm all ears for anyone's opinions on this.
0
Comments
-
systems with proper hydronic glycols or conditioners run in the 9-10 ph range The manufacturer of the chemical you used should have data to indicate appropiate levels Also a test kit to use along with their product?
In addition to the recommendations, make sure the fill or blend water is good quality, low hardness and TDS
Good chemicals and bad water may not get the results you expect.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
-
The deminerlizer cartridge will do about 35 to 40 gallons, it is mainly for adding some water after filling, while purging What is the total system volume? You’ll want to pull that hardness and TDS down some before blending in inhibitors if possibleBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Yes the caleffi unit is just for small water input. Installer used axiom puropal cartridges to treat after the fill before the inhibitors. We're guessing 75 gal total system which is 50 for turbomax, 5 boiler and 20 piping.
So it seems we should test water after more demineralization is done, then inhibitors.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements