Distillery Job
Berk
Member Posts: 1
I have a question for someone who may have piped a distillery. The condensate returns very low on the Mash tun and the still. without lifting both the still and the mash tun, I need to use a condensate return tank with pump to get the condensate back home. So my question is at around 10psi of steam will the condensate push uphill at least 4 inches to get in the tank. Also the inlet of the Mash tun is at the same height as the condensate return outlet. All my steam work has been residential boiler work. This is just messing with my head a little. Any help will be greatly apprecated.
Berk
Berk
0
Comments
-
Dan discusses this in Lost Art, chapter 10- "Sizing for Lifts to Overhead Returns". Your lift isn't that high- ISTR we lifted about 4 feet using 4 PSI or so on this job:
https://forum.heatinghelp.com/discussion/131461/metal-plating-plant-welded-header-repair-and-fuel-savings-update
Try to run that system at the lowest possible pressure that will work. It might surprise you when you find out how low you can go.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
@Berk You want to be sure you can vent the air and not create a water seal or the process will come to a grinding haltRay Wohlfarth
Boiler Lessons0 -
No it will not work if steam pressure is needed to lift the condensate. The condensate return tank needs to be vented so you can't have any steam in the returns IF you use a condensate tank. With a condensate tank you must have steam traps upstream of the tank.
If you do not have traps and have steam pressure in the returns then you can lift condensate depending on the steam pressure you have. 1 psi will lift condensate 24"0 -
Often hear about steam pressure required to blow condensate through trap. That is not how traps work.
My guess is that eventually owner will cut floor to make room for a receiver. Lifting the condensate will still be an issue. Best way always is to take advantage of gravity.EBEBRATT-Ed said:No it will not work if steam pressure is needed to lift the condensate. The condensate return tank needs to be vented so you can't have any steam in the returns IF you use a condensate tank. With a condensate tank you must have steam traps upstream of the tank.
If you do not have traps and have steam pressure in the returns then you can lift condensate depending on the steam pressure you have. 1 psi will lift condensate 24"0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements