1st company orifice
SeanBeans
Member Posts: 525
So I am assigned to install a condenser made by first company.
Was told to not use a TXV.. I pop open the installation manual and it says that the unit should be paired with an evap coil that’s fitted with a thermostatic expansion valve. As a result, subcooling is the process in which you charge the system.
Does this mean that it MUST be used with a TXV? Can an orifice be used?
first co’s tech support is closed for the weekend.
Attached is a photo of the install manual regarding charging the unit
Was told to not use a TXV.. I pop open the installation manual and it says that the unit should be paired with an evap coil that’s fitted with a thermostatic expansion valve. As a result, subcooling is the process in which you charge the system.
Does this mean that it MUST be used with a TXV? Can an orifice be used?
first co’s tech support is closed for the weekend.
Attached is a photo of the install manual regarding charging the unit
0
Comments
-
-
It's my understanding that charging a piston/orifice is rather generic, given return wet bulb & outdoor temps all the different mfgr's tables pretty much agree with each other. I have in my truck a slide calculator with 22 on one side & 410 on the other, my Fieldpiece digital will give a live superheat number with the right wireless instruments attached.
Agree with @EBEBRATT-Ed, why aren't you to use the recommended TXV?
0 -
The top reads 'Expansion valves and orifices must be calibrated and sized for use with R410a'. To me that says using the correct R410a orifice would be fine. Do you know the model evap? Some manufacturers offer swap out kits to convert to TXV.
Now the bottom states the WCX12 should have a TXV designed and calibrated for use with R410a. And subcooling is the charge method.
Is your condenser a WCX12? If yes, it looks like it requires a TXV. If its not, 1st. Co. says an orifice is ok.0 -
I always think of an orifice as kind of cheap! Orifice or cap tube systems (same thing really) are OK for relatively fixed temp systems like reach in coolers or household appliances where the condenser and evap are in a controlled environment and quite predictable. On a comfort cooling systems there are much more variables with condenser (outdoor) temps, and evap loading. A TXV is better at keeping superheat flat and efficiencies up.
We don't see heat pumps with orifices do we?Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
It’s a WCX120
-
> @SeanBeans said:
> It’s a WCX12
Then the paperwork says it requires a TXV. A kit might be offered. Cased coil? 🤞0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements