1st company orifice
SeanBeans
SeanBeans Member Posts: 525
edited May 2019 in THE MAIN WALL
So I am assigned to install a condenser made by first company.
Was told to not use a TXV.. I pop open the installation manual and it says that the unit should be paired with an evap coil that’s fitted with a thermostatic expansion valve. As a result, subcooling is the process in which you charge the system.
Does this mean that it MUST be used with a TXV? Can an orifice be used?
first co’s tech support is closed for the weekend.
Attached is a photo of the install manual regarding charging the unit
    EBEBRATT-Ed Member Posts: 19,602
    Most 410A units use expansion valve instead of orafices . Why not use an expansion valve? It's a better job and controls better.
    Solid_Fuel_Man
  • ratio
    ratio Member Posts: 4,176
    It's my understanding that charging a piston/orifice is rather generic, given return wet bulb & outdoor temps all the different mfgr's tables pretty much agree with each other. I have in my truck a slide calculator with 22 on one side & 410 on the other, my Fieldpiece digital will give a live superheat number with the right wireless instruments attached.
    Agree with @EBEBRATT-Ed, why aren't you to use the recommended TXV?
    HVACNUT Member Posts: 7,234
    The top reads 'Expansion valves and orifices must be calibrated and sized for use with R410a'. To me that says using the correct R410a orifice would be fine. Do you know the model evap? Some manufacturers offer swap out kits to convert to TXV.
    Now the bottom states the WCX12 should have a TXV designed and calibrated for use with R410a. And subcooling is the charge method.
    Is your condenser a WCX12? If yes, it looks like it requires a TXV. If its not, 1st. Co. says an orifice is ok.
  • Solid_Fuel_Man
    I always think of an orifice as kind of cheap! Orifice or cap tube systems (same thing really) are OK for relatively fixed temp systems like reach in coolers or household appliances where the condenser and evap are in a controlled environment and quite predictable. On a comfort cooling systems there are much more variables with condenser (outdoor) temps, and evap loading. A TXV is better at keeping superheat flat and efficiencies up.
    We don't see heat pumps with orifices do we?
  • SeanBeans
    It’s a WCX12
    > @SeanBeans said:
    > It’s a WCX12
    Then the paperwork says it requires a TXV. A kit might be offered. Cased coil? 🤞