Grounding

Why do I never see a hot water or steam system grounded? Surely, a hot wire in a wall can work loose and electrify a pipe and endanger the occupants?
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

Two btu per sq ft for degree difference for a slab

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,488
    The hot water or steam system (warm air too) is considered grounded by the circuit feeding the boiler or furnace. This may be a 15 or 20 amp 120 volt circuit in most cases. The ground can consist of a green or bare equipment ground run with the circuit conductors. Or the ground can be through the emt, ridged conduit, or other metal raceway correctly installed. In many cases with older systems even if the burner is grounded by the electrical circuit the boiler may not be (older floor mounted burners)

    Although the National Electric Code does not consider this as a ground most boilers are connected to a water pipe usually metal which is grounded at the electric service. The code requires the gas piping to be grounded but this is subject to local inturpratation

    The general rule is anything metal is supposed to be grounded if it is fixed in place older systems may not have caught up yet.

    There are cases where stainless steel sinks feed by plastic pipes and inspectors have made the electrician ground the sinks. Believe it or not "swimming pool" water has to be grounded
    Alan (California Radiant) Forbes
  • ChrisJ
    ChrisJ Member Posts: 16,316
    I agree with @EBEBRATT-Ed

    But, what does amaze me is aluminum siding isn't required to be grounded.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,488
    @ChrisJ
    I have herd (never done it) that aluminum siding is supposed to have jumper put on around the corners of the house.

    Another case of "accidental grounding" I guess. Light fixtures attached to it, outside outlets, meter socket??
  • HomerJSmith
    HomerJSmith Member Posts: 2,635
    Alan, perhaps you're not looking close enough. Everything that I see has a ground bonding screw except a W/H. The only grounding that I see on a gas line is for CSST. The thing is, you could have a 20 amp circuit breaker and have a leak to ground of 15 amps and never trip the breaker. I have checked the appliance with a meter for AC voltage (zero) to a good electric ground and also checked the ohms for zero.
  • JUGHNE
    JUGHNE Member Posts: 11,279
    If that 20 amp circuit was draining 15 amps into grounded/bonding piping, then the piping would not be a threat of electrocution. IMO.

    Hard to stay at the 15 amps without the leak becoming a dead short and then tripping the CB, but I get your point. Usually it would be a small current flow that would be dissipated by the bonding system.

    Some where in the National Electric Code (the book of exceptions BTY) it states that any metallic objects, be it piping of any sort, ductwork (isolated by canvas connectors even) shall be bonded with grounding wires sized to handle the largest circuit available in that area. Think of the electric range circuit of 60 amps as being the perhaps largest circuit in a house.
    Electric WH tanks are grounded by the circuit wiring. Gas WH bonded/grounded by the gas piping. Both may have insulating dielectric plumbing fittings installed so the water piping, H&C, needs separate bonding.
    Number 6 copper will bond up to 200amps.
    Number 4 copper will ground up to 200 amps.
  • HomerJSmith
    HomerJSmith Member Posts: 2,635
    "If that 20 amp circuit was draining 15 amps into grounded/bonding piping, then the piping would not be a threat of electrocution."--unless you provide a better ground thu your body.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,488
    If a 20 amp circuit is putting 15 amps to ground you would have no problem because the house would have already burnt to the ground.

    @JUGHNE

    I believe the code say something like " metal that may become energized should be grounded in accordance with the size of the circuit likely to energize it". So no need to ground everything to 60amps
  • JUGHNE
    JUGHNE Member Posts: 11,279
    Ed, as I am sure you know, you do what the AHJ wants.
    I had an inspector, that if the range wire ran the length of the house parallel to the piping, then we talk 60 amp bonding. Maybe #10 copper.
    If a machinal room with only 20 amp circuits then #12 would suffice.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,488
    @jughne,

    I don't like arguing with inspectors but I have no problem beating them over the head with a code book nicely when they are wrong.
    I find most all of them have been pretty reasonable with me over the years, but you have to know the code. They will often back down when they find out your reading the code book.

    Not that I am as up to date as I should be
  • Jamie Hall
    Jamie Hall Member Posts: 24,862
    I quite agree with @EBEBRATT-Ed -- and in the bad old days when I was doing inspections I always welcomed a knowledgeable contractor who knew the code and could help me understand it. Not to say all inspectors do...

    On the other hand... in some situations -- particularly if one is playing with gas or other flammables -- going slightly overboard on bonding (and grounding) isn't likely to hurt. Reason being that in some situations remarkably high voltages can be induced in pipes or other conductors by high current parallel wires (particularly if there are switching transients -- think contactors on big motors). Will this have enough energy to create a spark with enough energy to light off a leak? Don't know. Don't want to find out, either...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    edited May 2019
    Another good reason to avoid the glorified appliance connector knows as CCST! Gotta run a bonding conductor sized to ??? I do feel sorry for the natural gas guys who can't run soft copper though. Black iron sometimes doesn't lend itself well to old construction without opening things up. Using a material with excellent current carrying capabilities (copper or large steel pipe) is good safety.

    As far as grounding goes, all equipment I've installed has a ground screw/lug. The grounding conductor is sized per 2017 NEC 250.122. As a rule on #10 or smaller a full size (same size as current carrying conductors) is used. On circuits #8 and larger the table is used and a suprisingly small conductor can be used.

    The grounding conductor is sized so that if a bolted short to ground happens (dead short) a "reasonable" voltage drop happens and the over current device opens.

    I've never had to deal with sizing the grounding conductor to the largest circuit in a place, seems kinda ridiculous.
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • Jamie Hall
    Jamie Hall Member Posts: 24,862
    The smaller wire comment is good -- actually a small amount of resistance in the ground circuit is a good thing, oddly enough (although there is usually ample resistance for electricians not to have to worry about it). The resistance serves to reduce "ringing" and dismayingly high voltage spikes if a high voltage dead short occurs. It's a good tip for discharging large or high voltage capacitors, too -- it's better to discharge them by shorting with a 10 to 100 ohm resistor than it is to discharge with a dead short.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,488
    15 amp circuit=#14 ground. 20 amp circuit=#12 ground. #10 ground is good for up to a 60 amp circuit. #8 for a 100 amp circuit. Higher than that I would have to look it up.

    Keep in mind that the ground can also be emt, ridged conduit, greenfield or sealtight etc.etc. under certain conditions
    Solid_Fuel_Man
  • ChrisJ
    ChrisJ Member Posts: 16,316
    edited May 2019

    The smaller wire comment is good -- actually a small amount of resistance in the ground circuit is a good thing, oddly enough (although there is usually ample resistance for electricians not to have to worry about it). The resistance serves to reduce "ringing" and dismayingly high voltage spikes if a high voltage dead short occurs. It's a good tip for discharging large or high voltage capacitors, too -- it's better to discharge them by shorting with a 10 to 100 ohm resistor than it is to discharge with a dead short.

    Is this the Twlight Zone?

    Ringing?

    Jamie, are you feeling ok? :D

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Jamie Hall
    Jamie Hall Member Posts: 24,862
    Actually, I'm feeling fine... the reasoning is this: if there is even a small amount of inductance in whatever circuit is involved when you are trying to discharge a large or high voltage capacitor, the circuit will oscillate rather than discharge, unless there is some resistance to dissipate the energy. Which is what I meant when I referred to "ringing". Most of the capacitors we play with aren't big enough to be a problem, but the power factor compensating ones on industrial equipment are -- and so are the power supply capacitors in high fidelity power amplifies. So are cathode ray tubes (the capacity there isn't much -- it's just the plate -- but at 20,000 volts...)

    For equipment grounds, you don't want that much resistance -- you can figure the actual maximum allowable resistance if you want to (for instance, 8 oms for a 15 amp circuit, 6 for 20, 4 for 30 -- all assuming 120 volts to ground) but why bother? Code has you covered on that.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • ChrisJ
    ChrisJ Member Posts: 16,316

    Actually, I'm feeling fine... the reasoning is this: if there is even a small amount of inductance in whatever circuit is involved when you are trying to discharge a large or high voltage capacitor, the circuit will oscillate rather than discharge, unless there is some resistance to dissipate the energy. Which is what I meant when I referred to "ringing". Most of the capacitors we play with aren't big enough to be a problem, but the power factor compensating ones on industrial equipment are -- and so are the power supply capacitors in high fidelity power amplifies. So are cathode ray tubes (the capacity there isn't much -- it's just the plate -- but at 20,000 volts...)

    For equipment grounds, you don't want that much resistance -- you can figure the actual maximum allowable resistance if you want to (for instance, 8 oms for a 15 amp circuit, 6 for 20, 4 for 30 -- all assuming 120 volts to ground) but why bother? Code has you covered on that.

    Understood.

    However when it comes to equipment grounding I thought it all came down trying to maintain as low of resistance as possible vs cost.


    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Jamie Hall
    Jamie Hall Member Posts: 24,862
    True. I went off on a tangent. What else is new? :)
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    ChrisJSolid_Fuel_Man
  • nibs
    nibs Member Posts: 516
    Thought grounding was what they did in California to set their karma straight.
    Jean-David Beyer
  • Lots of crooked karma out here.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,599
    The Golden State Rule: “Do unto others.” >:)
    Yours, Larry
  • Jamie Hall
    Jamie Hall Member Posts: 24,862
    My karma ran over my dogma...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,599
    edited May 2019
    Ok, Just to stay off topic a bit more, it's fortunate that we don't all, always follow the rules o:)@Jamie Hall , poor dogma!

    Yours, Larry