HTP Elite 1st Gen FO6, then FO3, replaced return sensor, still F03

Options
wcs5050
wcs5050 Member Posts: 131
edited May 2019 in THE MAIN WALL
Went from erratic operation to none. Resistance across original return thermister dancing but seems ok. Anyone have any ideas. Primary pump operational.

Comments

  • wcs5050
    wcs5050 Member Posts: 131
    Options
    Skip that... Went back for followup eval... Not obvious, but flue gas temperature sensor under upper cover snapped and was sending vapor and moisture over upper control board. Integrated relay on board faulted.
  • Timco
    Timco Member Posts: 3,040
    Options
    Hello,

    We have a TSB regarding this issue, and if you email us at techsupport@htproducts.com or call us at 800-323-9651 we can send you the entire kit needed (7450P-901) to replace the exhaust flue assembly and the flue temp sensor. Sorry to hear you had this issue. I only check in every 2-3 days so I missed this post. Tim