Steam trap? And tune up
billtheplmbr3845
Member Posts: 41
Does this device function as an air vent. The system pressure is currently set at 5 psi. Most of the vents are spitting water. I want to turn the pressure down to approximatly 1/2 psi, change all the steam traps, air vents ,and the f&t traps. The system has been neglected for a number of years. The steam mains are 6 inch and 3 inch. Any thoughts or suggestions would be appreciated. Thanks in advance
0
Comments
-
Yes it is a vent, and probably will enable the system to maintain a vacuum as well. There are probably crossover traps from the end of main to the return, which may be inoperative.
Definitely turn the pressure down to 8 ounces maximum as well. You may need a vaporstat, and a low pressure (0-3 psi gauge, to verify the pressure.—NBC0 -
Agreed. I'll bet it's stuck closed or only partway open, and that's why someone cranked the pressure. Looks like it was added after the system was first installed, since the pipe it sits on is welded to the main.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements