Steam trap? And tune up

Does this device function as an air vent. The system pressure is currently set at 5 psi. Most of the vents are spitting water. I want to turn the pressure down to approximatly 1/2 psi, change all the steam traps, air vents ,and the f&t traps. The system has been neglected for a number of years. The steam mains are 6 inch and 3 inch. Any thoughts or suggestions would be appreciated. Thanks in advance

Comments

  • nicholas bonham-carternicholas bonham-carter Posts: 7,861Member
    Yes it is a vent, and probably will enable the system to maintain a vacuum as well. There are probably crossover traps from the end of main to the return, which may be inoperative.
    Definitely turn the pressure down to 8 ounces maximum as well. You may need a vaporstat, and a low pressure (0-3 psi gauge, to verify the pressure.—NBC
  • SteamheadSteamhead Posts: 13,125Member
    Agreed. I'll bet it's stuck closed or only partway open, and that's why someone cranked the pressure. Looks like it was added after the system was first installed, since the pipe it sits on is welded to the main.
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
Sign In or Register to comment.

Welcome

It looks like you're new here. If you want to get involved, click one of these buttons!