Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!

Old Timken Burners

Options
CarbonDave
CarbonDave Member Posts: 9
To update an older post, shown below, I've added a video of the furnace in operation. An old Peerless coal furnace #123 that was converted to burn kerosene or #2 using a Timken rotary wall burner.

https://forum.heatinghelp.com/discussion/138226/old-timken-burners

https://www.youtube.com/watch?v=JkTjsW6M6AM

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,711
    Timken was an excellent burner and burned with high efficiency.
    Boiler looks to be in good shape and well cared for.

    Hope it holds together because parts for those burners are probably long gone. Vertical rotary burner
  • Intplm.
    Intplm. Member Posts: 3,113
    Thanks @CarbonDave . Sure did enjoy it. "Rotary motor", "swirl action flame". Can't help but think this is a predecessor to the modern day oil burner.
  • HVACNUT
    HVACNUT Member Posts: 7,584
    edited April 2019
    I've heard the name Timken but never saw one. Come to think of it, I still haven't seen one. Any video or pics with the mechanicals?
    Very cool though.
  • Steamhead
    Steamhead Member Posts: 18,770
    It was one of several types of burners offered in the early days. A variation of this type didn't use a hearth around the rim, but burned the flame in suspension just short of the walls.

    Then there were the vaporizing pot-type burners, which heated the oil so it would vaporize and burn like a gas flame would. ISTR these were very difficult to adjust so they burned clean, and would often create a lot of soot. Some of these relied on natural draft but others used fans.

    The burner configuration we know today was called the gun type. The high-pressure variation worked much the same as today's burners, and there were also a couple of low-pressure types. I fondly remember the Winkler, but Williams also had a low-pressure type called the Oil-o-Matic and there were a couple others too. Along the way, several improved burner head designs such as the Shellhead led to better efficiency and reduced sooting.

    I have read somewhere that Carlin was the first to offer the flame-retention head that we use today, about 1969. This type will run all year without sooting if it is set up properly. Think about that next time you're sucking soot out of a boiler with a current-model burner................

    All Steamed Up, Inc.

    Baltimore, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting

    Intplm.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,711
    edited April 2019
    @Steamhead
    I think Carlin was the first but they all jumped on the band wagon about the same time. I started in 73' and they had been out a little while so 69' is probably right.

    I think the shell head started it, also there were a few 1725rpm burners that were pretty good as well in the 60s. Some of the old stuff was a nozzle on a pipe with a little spinner or turbulator which didn't do much. Torrid Heat was another vertical rotary

    Iron Fireman was the first I think with forced draft flame retention back in the late 50s. They ran 3450 motor and 300# pumps back the. It took the residential market a long time (too long) to catch on...especially with the oil pressure. With and old burner that was the first trick to try to make it burn better drop the nozzle and raise the pump pressure. It was in Burkhart's book.

    My sister bought a house with a pot type burner in a furnace. I made her change it before the first winter. Those things had to burn #1 or kero. Had a customer at the oil company that moved and bought a house with a pot burner. He didn't know and ordered oil for it #2 oil. He didn"t live their for a month or so because he was traveling...what a mess when he came home.

    Both those furnaces were made by "Perfection" or "Perfection grate and stoker" something like that.

    They also used to put the 275s on really long legs. Pot burners had no pumps and relied on gravity flow
  • Jamie Hall
    Jamie Hall Member Posts: 27,644
    The burner in the big (I do mean big...) HB Smith that was originally in Cedric's home was a Quiet May. So called. I wasn't paying too much attention at the time, so I can't tell you much about it -- except that it was anything but quiet. And the efficiency wasn't that good either (it burned 5 gallons per hour to do what Cedric does on 2.75).
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Steamhead
    Steamhead Member Posts: 18,770
    Quiet May was based in Baltimore, and I frequently see buildings their burners once heated. They had their own emergency switch plate design, as did Esso. I recently found what looks like a complete wall-mounted primary control from a QM, and will try to sweet-talk the owner into letting me salvage it.

    All Steamed Up, Inc.

    Baltimore, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting

  • JUGHNE
    JUGHNE Member Posts: 11,617
    A few Timkens made it to this area. The dealer was a frequent traveler to the Eastern states and must have been impressed.

    "Silent Automatic" was another name for these units.

    I changed out the few I have seen, to NG or HP.
    Did the furnaces use a stack switch for oil safety control?

    There was one oil fired water heater I replace the ignition transformer on.
    The safety was an over flow spout inside the burner pan, if enough oil built up from not igniting, it would run out into a small cup attached to an arm/lever. The weight would then tip the lever that the other end was connected to the mechanical switch that would shut off the oil flow to the motor/pump. To reset you had to empty the cup and reset the small oil flow lever.

    The shaft of the motor had spiral groves that would lift the oil and push it out the arm nozzle ends.
    IIRC, you could raise and lower the oil flow control physically to get the gravity flow just to the pick up point of the motor shaft.

    The rotating spray arm reminded me of a early Scotsman ice machine. (troublesome to service).
    HVACNUTCTOilHeat
  • Pughie1
    Pughie1 Member Posts: 136
    yes, they required stack mounted primary controls, had to be careful though, couldn't use the Hwell Ra 117A's. had to use a control with a timed ignition sequence, the old general/perfex or the White Rodgers 610 series come to mind.
  • CarbonDave
    CarbonDave Member Posts: 9
    Glad the video was enjoyed. I do all of the service / maintenance because I haven't found anyone that knows how to service this unit. Here are a few pictures of the rotary burner motor, vanes and distribution nozzles. The setup I have doesn't have the float shown in the pictures. It uses a solenoid controlled adjustable needle valve for fuel regulation. Gravity feed from a "day tank" mounted on the wall, pulling fuel from a storage tank.
  • HVACNUT
    HVACNUT Member Posts: 7,584
    > @Pughie1 said:
    > yes, they required stack mounted primary controls, had to be careful though, couldn't use the Hwell Ra 117A's. had to use a control with a timed ignition sequence, the old general/perfex or the White Rodgers 610 series come to mind.

    I've only serviced one Iron Fireman burner. Residential. I dont remember the boiler.
    Middle of the night no heat call. I replaced the owner supplied belt.
    The next time I went there was to follow up on the install dept who that day installed a Buderus G215 with a Riello.
    The RA117A was an interrupted ignition primary as you know. The IF primary differs using sequential ignition. Does it use a standard burner transformer? Typical electrodes? Assuming the belt drives the fan, how does it provide the timed ignition? Switch somewhere on the fan assembly or shaft?
    What brand primary? 90 seconds?
    Do you or anybody have a schematic?
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,711
    @HVACNUT
    The only iron fireman resedentials I remember they made some regular gun type burners which were pretty much the same as everyone else and they did have a "Mark II" ? burner that came on a steel boiler that they sold in the 60s...never really caught on...was some type of weird burner don't remember much about it could have been belt drive
  • Pughie1
    Pughie1 Member Posts: 136
    From my memory the iron fireman used a Honey well Ra 187 or RA 890 type electronic relay with a photo cell. yes they had a belt drive fuel unit. I was referring to the Timkens when I was talking about timing the ignition sequence. The RA 117's cut the ignition off as the helix on the stack control heated up as flame was established. Very often before the flame had made it all the way around the flame ring. this would cause the flame to snuff out. Wonderful burner when adjusted and running correctly. We used Kerosene almost exclusively since it was much easier to ignite and vaporize
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,711
    RA117A when it shut of ignition it meant the flame was proven. helix moved with the heat then the ignition shut off.

  • mattmia2
    mattmia2 Member Posts: 17,753
    I know Timken as a bearing manufacturer.

    When I bought my house it had a Perfection Stove Company gas furnace that said "approved for gravity use only" but appears to have been installed new with a separate blower cabinet. It was installed around 1950. It had another brand name on it which I don't remember now, it might have been Peerless.
  • RonnieJ
    RonnieJ Member Posts: 46
    Thanks for the video @CarbonDave! My brother and I used to own a two-family home built in 1866. The 1st floor apartment had a Timken rotary burner in the base of a hot air furnace. That had to be the coolest thing I ever saw. It ran well for several years until we had a problem with a weak transformer where it wouldn't ignite. If I opened the door, and placed a paint stick against the outside rails, the oil and sparks would collect and eventually ignite, restoring heat until the tech arrived.

    It had a heat exchanger that looked like the containment dome on a nuclear reactor. When we finally replaced it, we found corroded transformer connections that were the ultimate cause of its problems. They were just spring clips on fairly thick gauge wire. If we knew what we were doing, we probably could have gotten a few more years out of it. Our tech had no idea how old it was - 1940's? It had clearly earned the right to die. Whoever designed them was creative, indeed!

    Found this on the web - it shows the stainless ring and you can see the igniters at the 9 and 3 o'clock positions. You really have to appreciate well-built mechanicals - they are the fruit of genius.


    Energy Kinetics EK, Goodman GSXC72400, SpacePak ESP 2430J
    HVACNUTmattmia2
  • clammy
    clammy Member Posts: 3,257
    When I did oil we had one community just loaded w them all w remote wall mount oil pumps .usually always had oil supply issue when the furnaces where update mostly had to add on small tank tank set up or when we got luckily they had gas n we would do a conversion ,these where post war homes and all slab not good memories .i do have the timkin manuals giving to me by a ole timer many years ago peace and good luck clammy

    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    Specializing in steam and hydronic heating

    HVACNUT
  • FranklinD
    FranklinD Member Posts: 399
    The original boiler in my folks’ house (gravity hot water) was a “Silent Automatic.” Still have the tin wall plate of instructions for it. That boiler is long gone, of course, but the “Day tank” and pump is still mounted high on the basement wall nearby. The original in-ground oil tank was removed about ten years ago...they thought it was a 1000 or so gallon tank, but it turned out to be over 3000! Wow did they have a helluva time getting it out from between my folks house and the neighbors. They started digging at the fill pipe and found an entire manhole cover of sorts 18” underground. The cover was bolted in place and sealed with what looked like lead & oakum, but I’m not sure. The contractor had to cut the tank into three sections to get it on his trailer...it was riveted together, if I recall correctly. My mom took pictures of the whole process. And yet...the Day Tank & pump remain.
    Ford Master Technician, "Tinkerer of Terror"
    Police & Fire Equipment Lead Mechanic, NW WI
    Lover of Old Homes & Gravity Hot Water Systems
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,711
    @FranklinD
    Never saw a riveted oil tank before but I wouldn't doubt it. Must have dated back to the 1920s.

    The early 20s oil was just getting started. Welding also was getting started during WW I but didn't really get going until the late 1920s.

    Took out and old HRT steel boiler once the name plate was 1927 or 1929. When we got the covering off it we found the shell had riveted construction
  • FranklinD
    FranklinD Member Posts: 399
    @EBEBRATT-Ed - the house was built in 1892 or so (that’s one detail the title abstract isn’t clear on) and the boiler was originally coal fired. The oil burner system was installed in the 20’s to early 30’s but that’s as close as we can get to a date. I’ll be over there again tomorrow so I’ll snap a few pictures of the Silent Automatic instruction wall plate and the day tank. The tank and pump are in pristine condition and I’d bet they still operate (last in use for the winter of 1997-1998, then drained). I’m not sure if Mom has pictures of the old boiler; I’ll be sure to ask. I know she has an album of the tank removal.
    Ford Master Technician, "Tinkerer of Terror"
    Police & Fire Equipment Lead Mechanic, NW WI
    Lover of Old Homes & Gravity Hot Water Systems
  • FranklinD
    FranklinD Member Posts: 399
    As for riveted tanks, the house is about 3/4 of a mile from the local Frasier Shipyards (still in operation), so it doesn’t surprise me that a riveted tank was used - it probably originated from the shipyards. I live in Superior, WI, way over at the far western tip (“arrowhead”) of Lake Superior, “Where Rail Meets Sail” as they say. Lots of industries have come & gone here over the years, and a lot of history is literally just sitting around in piles in certain areas of the city.
    Ford Master Technician, "Tinkerer of Terror"
    Police & Fire Equipment Lead Mechanic, NW WI
    Lover of Old Homes & Gravity Hot Water Systems
  • Big Ed_4
    Big Ed_4 Member Posts: 3,557
    edited May 2019
    Last Timkin I worked on was in the late 70's and the owners did not want to give it up . Timkins really were not safe . They relied on an old spill switch , old stack relays and no cracks in the man made hearth. It could be possible to be burning on one side and leaking out raw fuel on the other side or underneath the hearth. And those old supply tanks with a buried tank . Single iron pipe with a foot valve . Try freeing up a plugged foot valve on a cold winter night ,....They don't make them like they use to ,and sometimes you have to say thank God ....

    There was an error rendering this rich post.

  • FranklinD
    FranklinD Member Posts: 399
    Good grief, finally got over to my mom’s place and took the pics I promised. The Silent Automatic instruction placard (tin) and the day tank on the wall. And a pair of supply/return take-offs on the basement mains. One pair feeds a first floor rad, the other pair feeds a second floor rad.
    Ford Master Technician, "Tinkerer of Terror"
    Police & Fire Equipment Lead Mechanic, NW WI
    Lover of Old Homes & Gravity Hot Water Systems
  • HVACNUT
    HVACNUT Member Posts: 7,584
    That's awesome. Its amazing how years ago every homeowner new their heating system because they had to. Now your lucky if the know where the emergency switch is.
  • FranklinD
    FranklinD Member Posts: 399
    While I was there I happened to mention to her that it’s a shame she didn’t have the gauges from the old boiler... lo and behold she pulled a box off of a shelf next to the “new” boiler and there they were! She said the heating company left them there for us after they broke up the old snowman with sledgehammers. The glass is cracked on the altitude gauge but the other (temp gauge) is in good shape. Cool that it has the supply house name on the face...Duluth is right across the bridge from me, though when it was installed it likely would’ve come across by barge.
    Ford Master Technician, "Tinkerer of Terror"
    Police & Fire Equipment Lead Mechanic, NW WI
    Lover of Old Homes & Gravity Hot Water Systems
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,711
    @FranklinD
    The picture that shows the piping take offs, the cast iron tees on the main with the ribs on them....those are really old fittings
  • FranklinD
    FranklinD Member Posts: 399
    @EBEBRATT-Ed
    Yessir, her house was built in about 1892. It is a beauty...I was born there and grew up there and my moms been there by herself since my dad passed in 2003. It’s a full 3-story 7 bedroom farmhouse-style place. She’s preparing to sell and move to an apartment (she’s been saying that for 5 years now, heh). I fear that it’ll get snapped up by a local slumlord developer to be turned into student housing since she lives directly across the street from the local University of Wisconsin campus. And I mean it - 200ft to the front doors of the administration and science buildings. I’d love to buy it - I’ve always wanted to - but sadly it just doesn’t make sense for my family now. I do a lot of automotive work out of my little garage/shop, and her corner lot has zero room to expand her tiny attached garage (it was literally a carriage house when added in 1908). Anyway, the gravity heating system is a beauty - big mains, ornate cast iron radiators on all three floors, original riveted expansion tank in the attic (no longer used)... I love that house and always will.
    Ford Master Technician, "Tinkerer of Terror"
    Police & Fire Equipment Lead Mechanic, NW WI
    Lover of Old Homes & Gravity Hot Water Systems
  • FranklinD
    FranklinD Member Posts: 399
    I ended up buying a 1914 Foursquare across town from her, also with an original gravity hot water system (though mine wasn’t original like hers - I’ve had to do some work to get it performing properly again after years of hack work). Every year we tackle another project - this year will be painting the outside, restoring some more of the original wooden double-hung windows, and hopefully repairing the front porch. It’s a labor of love!
    Ford Master Technician, "Tinkerer of Terror"
    Police & Fire Equipment Lead Mechanic, NW WI
    Lover of Old Homes & Gravity Hot Water Systems
  • Gabriel82
    Gabriel82 Member Posts: 39

    hello everyone! Can someone with experience and knowledge explain me why rotary oil burners(vertical or horizontal) are not manufactured today in small size?

    Except Sunflame but those are for big ships

    http://www.sunflame.net/english/core/010/

    Seems to me they are more versatile ,ni blocked nozzles ,can easily burn thicker fuel oils.

    I dislike pot style burners ,because of the constant cleaning one must do(almost daily).

    But am disgusted by the complexity and maintenance of forced draft gun burners .

    Although Riello 40 G5RK is decent ,used one for awhile and having an oil preheater is nice.

    But if any dirt gets in oil it will result in problems...

    Especially if it gets past the filter...

    Now I'm back to wood burning in ceramic tile stove with natural draft 😎

    Besides the manual work to prepare cut split wood logs ,no problems so far!

    And I don't care of the ceramic tile stove's efficiency. So far 🙄

    But am always drawn to the rotary oil burner. seems so nice and simple yet ignored completely or almost extinct.

    Thank God for Sunflame company and their products!

    Thank you all in advance for your answers.

    Had no ideea Timken built burners like these in past!

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,711

    They say rotary burners could not pass the pollution test. The older ones could not but newer designs came out that can

    Gabriel82
  • Gabriel82
    Gabriel82 Member Posts: 39

    @EBEBRATT-Ed I understand.

    Old vs new "controversy"...

    I only know of Sunflame when it comes to these burners.

    Also, I saw one video of a burner like this but direct drive. (not belt)

    Seems to be the only one on youtube.

    And its not even functional. Uploaded 3 years ago and it needed a pump rebuild.

    Was burning bunker oil C type(whatever that is... here in Romania we have fewer choices for heating oil).

    Mostly natural gas or wood stoves. Like ceramic tile ones.

    But its a lot of hard manual work.

    If natural gas prices go up since this Russia vs Ukraine war is not anywhere near "end" a lot of people will look for wood or coal.

    I've given up on oil because of debatable quality , minimum ordering quantity and the problems with gun type burner ,plus maintenance!

    Natural gas central heating(and instant hot water) plus hard wood is cheaper and less maintenance!

    But since I love fire (even use a gasoline Shmel-2 cooker/burner), I'm still drawn to an oil burner.

    Rotary burner would be my second choice after natural gas or wood.

    Installed in a NTI Caprice 85 or similar boiler ,it would also provide hot water.

    Very atracting.

    If you can/want or know please tell me what are "newer design" rotary burners?

    Thank you!

  • Big Ed_4
    Big Ed_4 Member Posts: 3,557

    The selling point in selling the Timkin burner and low pressure burners to coal burners , was noise and being automatic . They relied on gravity feed oil , lift pumps and oil tanks on 4' tank legs ..

    With crappy oil maybe look into a waste oil style burner , they use a metered pump to deliver the oil with preheaters and compressed air to help atomized the oil for combustion ..

    There was an error rendering this rich post.

  • bburd
    bburd Member Posts: 1,324
    edited January 27

    "Bunker C" is the nautical term for Number Six heavy residual fuel oil. It is not used much today because of environmental restrictions—it produced air emissions similar to bituminous coal. It is so viscous at room temperature that it must be heated in the storage tank, and further heated to burn. It was used in very large boilers on ships and in electric generating stations, large buildings, factories and district heating plants.

    Its advantages were higher heat content and lower cost than lighter fuel oils. It made economic sense in larger installations where the lower fuel cost could offset the additional capital and maintenance costs.


    Bburd
    Gabriel82