Condensate and condensation pump

matt74
Member Posts: 9
I have 1 pipe system in a 15 unit apartment that was built in 1878 in St Paul MN and I have a issue with over condensation that will overfill the boiler and the boiler will shut off I have replacing steam vents inside the and traps and it still over condensate
0
Comments
-
What pressure are you running?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Limit it set at 2 1/4 operation is set at 2 1/20
-
Pressure is too high, but not hopelessly outrageous. The system will probably run just fine cutting out at 1.5 psi.
That said, condensate pumps are an invention of the Devil, intended to annoy and upset people managing steam boilers. You need to modify the system, so that the pump, which will now be a boiler feed pump, is controlled by the level of water in the boiler, not the level in the condensate receiver. Then the level of water in the condensate receiver will control an automatic water feeder, but you will need to have an overflow line on the condensate tank to a handy drain somewhere.
You also need to find out which safety is shutting the boiler off on an overfill. It's a good idea to do that, but it might be nice to know what is doing it.
You may also have problems with slow condensate return. If you can, flushing any wet returns might prove helpful.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Your fresh water auto fill could be passing water thru or over reacting when the water level drops before water returns.
As said above, your return lines could be slow causing the auto fill valve to respond.
Your pump is controlled only by it's own float....not by the boiler??0 -
Get a low pressure (0-3 psi), gauge from Valworx, and verify the pressuretrol is cutting out at setpoint.
2.5 psi can push the water level in the wet returns up 70 inches, temporarily starving the boiler of water, causing any auto feed to activate, and blocking the air from escaping. If you ever have to replace the boiler, consider reconfiguring the returns to gravity.—NBC1 -
-
Did this problem happen after a boiler replacement or has it developed over time? What system updates have been done to this system?0
-
Ever since they cut out the old gravity lead and added the condensation pump0
-
-
This is not a coincidence...matt74 said:Ever since they cut out the old gravity lead and added the condensation pump
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Does anyone know why the pump was added; what problem was trying to be solved?
Perhaps slow returns then. Maybe the thought was the extra reservoir/accumulator would put more water into the system as it boiled away.
This boiler looks to be shorter than the original. Lower water line might have made some wet returns dry?0 -
LOL.. almost every steamer I see in Denver had a condensate pump on it0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 941 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements