Comment on this 4-Boiler Hot Water Setup
zackwatt
Member Posts: 81
I'm doing a walk through on a potential property tomorrow, and it has hot water heat. 4 units, 4 boilers. I've got steam in my house, so i'm pretty familiar with what to look for on steam boilers, but hot water is entirely foreign to me. I know this photo doesn't show a lot, just wondering what jumps out...either good or bad? Thanks!
0
Comments
-
can't open the photo0
-
Got time to make a sketch of the piping arrangements? Particularly with attention to where pumps are, and valves, and the expansion tank -- and comment on whether all four are the same? Or at least photos showing all the piping for a typical installation?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Maybe try this:EBEBRATT-Ed said:can't open the photo
https://photos.zillowstatic.com/cc_ft_1536/ISe8fldcin1h6x0000000000.webp0 -
Looks like the #4 boiler is new and not original like the other three ?. Might be a indication that the others will soon need replacing ??0
-
Isn't #4 original and the other 3 newer?0
-
One new. Three older. Look at the circulators. The tridicators. See the yellow "Energy Guide"?0
-
Take another picture showing the ceiling. I'd like to see how they are vented.
Is this an original 4 unit building or converted?
What are the green things above each boiler, expansion tank? They look like old water hammer arrestors.
Of course if any replacement is to be done, a proper heat loss so as to not oversize.There was an error rendering this rich post.
0 -
Thanks for the replies, this is just off the listing. I am heading over to the property in the next hour. We'll see what we find...0
-
0 -
According the Weil Mclain CGA Gold installation manual, the closed expansion tanks this system has should not have automatic air vents on the boiler, as it can case water logging of the expansion tank. I'm assuming the green devises on top of each boiler are just that...automatic air eliminators.0
-
The green things at each boiler are auto air vents, they have the small tubing to direct any water spurts away from the boiler.
They do not belong on a system that has the compression tank that hangs near the ceiling. They will eventually vent all the air out of the system leaving the comp tank with none and it will become water logged.
The combo relief valve and pressure reducing valves that I see are about the age of the comp tanks. But each boiler has it's own relief valve.
Without a valve between the tank and boiler piping you have to drain the entire system to get water out of the tank.
Does each system have cast iron rads?1 -
There appears to be no isolation valves on these units as @JUGHNE mensions. This makes for a very tough service call. I would add isolation valves to each boiler so each boiler can be serviced independently without troubling the other living areas.
As it is now, if one boiler needs service all the boilers and units would potentially be affected.0 -
I must be missing something...as there seems to be 4 of everything, expansion tanks included. I'm not seeing how one boiler service would disrupt the other 3 units.Intplm. said:As it is now, if one boiler needs service all the boilers and units would potentially be affected.
0 -
The venting is not correct. It is supposed to be Y connections from each boiler. I hope that there is a liner in the chimney.0
-
Is there a gas hot water tank to the left of the boilers?0
-
I assume that each heating system is separate with own comp tank, fill valve with cold water supply stop and gas service.
I don't follow how the service of one boiler would affect other units?
True, isolation valves on supply and return for pump changes etc. would greatly simplify that process.
However with only 4 CI rads to drain down and then bleed air out of, although a PITA, it could be worse.
The valves I refer to are to isolate the compression tank from the system and drain any water logged tank while keeping the system full of water. Of course a hose bib must be installed.
0 -
On the water side of the boilers. If there is a leak in one of the units, all of the units will have to be drained and restarted because there are no isolation valves installed for each unit , and no isolation valves are installed on each boiler. For example. If there is a leak on the system in unit 2, units 1,3 and 4 will have to be shut down as well as unit 2 because there is no way to isolate the the four systems as shown.zackwatt said:
I must be missing something...as there seems to be 4 of everything, expansion tanks included. I'm not seeing how one boiler service would disrupt the other 3 units.Intplm. said:As it is now, if one boiler needs service all the boilers and units would potentially be affected.
0 -
In other words. All of the units would be without heat if only one unit had a leak or similar repair needed.0
-
What do the 4 units share that water drain down in #2 would require draining of 1-3-4?0
-
-
Is there a diagram somewhere of how it should be?STEVEusaPA said:That venting is extremely wrong and doesn’t meet code. Can’t believe it works.
I wouldn’t walk into that mechanical room without my personal CO monitor on.0 -
They are all connected as one source. At least from the picture as they are piped. They do not look like they are seperated per unit. At least that's what i can see from the pictures. They do not look like they are seperated from one another. They look like all four boilers are acting as one boiler.0
-
More pictures are needed but the best thing to do is have a expert physically in the basement to verify this.0
-
There’s no diagram, but there is a code book.
There was an error rendering this rich post.
0 -
How many electric and gas meters for the building?0
-
You may have actually won in the long run.zackwatt said:
Thanks for the comments guys, I actually lost out on my offer on the building. So on to the next one! I need to pick up Dan's book on Hydronics next...
There was an error rendering this rich post.
0 -
I would assume that each boiler has its own return and supply piping, and that a leak on #1 wouldn’t share any water pipes with #2 except where the cold water comes in0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 418 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 59 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.2K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements