Grundfos Alpha 2 Wiring
Le John
Member Posts: 237
I want to wire the Alpha 2 to a Taco Zone Valve controller and since the alpha's display is always on what is the recommended method to wire it to the Zone Valve controller?
0
Comments
-
If you turn off the pump, the auto adapt feature will reset each time. What you are suggesting will work just fine in the constant pressure or fixed speed modes. Just cut the cord end off and wire it to the controller."If you can't explain it simply, you don't understand it well enough"
Albert Einstein2 -
I too like to see everything turn off when not in use!Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
-
On the ZVC 404 isn't the power to the circulator interrupted when there is no call for heat? How would the display illuminate when there is no call for heat?0
-
You can leave the Alpha 2 powered up all the time, that's why they have the version with the line cord that you can plug in. The Alpha 2 will slow down and stop as the zone valves close. I use it like this on my boiler. The Alpha 2 does have memory as well for on and off applications. I have used it like that as well.0
-
thank you @SuperTech - I can add an outlet for the pumps line cord but how will that get wired to the ZVC404?0
-
-
-
-
I've done it both ways, cut the cord and wire to a control of some kind or simply plug it into an outlet. If you wire it to a control it will wake up to a brand new system every time it's powered and have to relearn that system over and over again. If 6you simply plug it into an out let it will power down when there is no call and retain its adaptive memory. It really should have a constant power supply. With all the zones closed you'll see that it's using no or very little power and moving no water the way it was designed.
Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
1 -
If its being used in a zone valve application, it shouldnt be in the autoadapt mode, it should be in the constant pressure mode so there is nothing to learn.
the autoadapt mode should be used with thermostatic radiator valves.
So powering down after use will not affect the performance of the circ.
5 watts is still 5 watts.
Dave H.Dave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
1 -
I agree, I dont like the deltaP pumps running at a minimum speed just waiting for a valve to open. I'd rather power it down.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
@Solid_Fuel_Man if using the plug - does that mean the pump is always running even though the zone values are closed? With all zone values closed is it actually moving any water?Solid_Fuel_Man said:I agree, I dont like the deltaP pumps running at a minimum speed just waiting for a valve to open. I'd rather power it down.
0 -
Yes, it is spinning. Not moving any water, its keeping the differential pressure to "see" when a valve opens. Otherwise it's just a pump upstream of some valves.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
Another option was to wire it through a Caleffi relay which will exercise the circulator occasionally throughout the "off" season.
Possibly some of the boilers also have that exercise function built into their on board controls?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
The Honeywell L7224U has pump cycling built in, as does many condensing gas boilers0
-
Doesn’t the Taco ZVC have this built in to the control? It is wired to a Lochinvar Noble Combi.0
-
Usually there will be a DIP switch on the board to enable an exercise function. Here are DIP switch options on the Caleffi ZVR, it varies from brand to brand, as to the features and functions..Le John said:Doesn’t the Taco ZVC have this built in to the control? It is wired to a Lochinvar Noble Combi.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Shouldn't let the pumps "rub" for 30 seconds after 72 hours of non operation😁 think I found a typo hot rod.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements