Breakdown of CFA in one-pipe parallel system

FizzFizz Posts: 494Member
Front: supply main with 133.5 attached rad; 31' of 11/2" and return main(steam filled to vents) 28.5' of 11/2" pipe=tot pipe CFA of .83, rads have 3.34 CFA.
Back: SM, 84sf of att rad,; 28' of 2" and return main 26.5' of 11/2" pipe=tot CFA .99, rads have 2.12 CFA.
Considering above, what would be proper main venting? Currently has MOM1 and G2 on front and 2 MOM1's on back.

Comments

  • nicholas bonham-carternicholas bonham-carter Posts: 7,817Member
    Try an additional Big Mouth on each main, for a start.
    Remember you are trying to balance the resistance of escaping air, (back pressure), with the aggregate back pressure of all the rads on each main. That way steam will take the easy way, and fill all the main pipes first, and then move up into all the radiators,
    This is why we suggest venting the mains fast, and the radiators more slowly, so steam arrives simultaneously.
    On your good low pressure gauge, you should see the starting air removal take place at less than 2 ounces pressure.—NBC
  • FredFred Posts: 7,815Member
    What size tapping is on each main for the vent(s)? You can keep adding vents but there is a limit on the capacity of the tapping as well and exceeding that is just wasting money.
  • FizzFizz Posts: 494Member
    Fred,tappings are 1/2". NBC, how big are big mouths? Don't know if have enough room.
  • ethicalpaulethicalpaul Posts: 664Member
    Big mouths have 3/4" threads and they need maybe 5"-6" of vertical space above the pipe


    1 pipe Utica 112 in Cedar Grove, NJ, 1913 coal > oil > NG
  • FizzFizz Posts: 494Member
    Thanks Paul!
  • SteamheadSteamhead Posts: 12,872Member
    From what you posted, it looks to me like you already have the vents you need.

    Rear main has 0.99 CF, and a Gorton #2 is good for 1.10 CFM at one ounce pressure. Front main has 0.83 CF, and a single MOM #1 is good for 0.333 CFM, so the three you have would equal 0.999 CFM. I'd try installing the vents as indicated here and see how well it works before buying anything else.
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
  • FizzFizz Posts: 494Member
    Will do; thanks Steamhead!