I have a Condensing gas fired wall mounted boiler does DHW, radiant floors as well as central heat
ggparts
Member Posts: 3
The brand is Baxi Luna 1.330 Recently I have noticed the gauge on the front of the unit has been indicating higher pressures. (I not even sure what it measures)
range of the gauge is 0 - 4 bars with the operating range (green area) 1 - 1.5 ish.
Although everything seems to be operating fine the gauge is showing well into the red at 4 +
I am hoping to find the cause of the high reading. Possibly a failed gauge ?
Any advice I can get before calling some on in would be appreciated. I don't want to find the basement full of water
range of the gauge is 0 - 4 bars with the operating range (green area) 1 - 1.5 ish.
Although everything seems to be operating fine the gauge is showing well into the red at 4 +
I am hoping to find the cause of the high reading. Possibly a failed gauge ?
Any advice I can get before calling some on in would be appreciated. I don't want to find the basement full of water
0
Comments
-
-
To find the small expansion tank what would I look for?0
-
Take a look and see how the pressure changes from when the unit is cold -- let it sit off for a couple of hours -- and then as it warms up. Shouldn't change that much -- half a bar, perhaps.ggparts said:To find the small expansion tank what would I look for?
Also... how is water added to the system? If it's through a pressure reducing valve, that valve may be leaking past.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
This is the only source of heat for my home, I hesitate to turn it off. Not sure if there is a PRV or not.Jamie Hall said:
Take a look and see how the pressure changes from when the unit is cold -- let it sit off for a couple of hours -- and then as it warms up. Shouldn't change that much -- half a bar, perhaps.ggparts said:To find the small expansion tank what would I look for?
Also... how is water added to the system? If it's through a pressure reducing valve, that valve may be leaking past.0 -
I agree... you heat water and it expands thus pressure goes up. Something is preventing the expansion tank from working or the expansion tank isn't working.
0 -
Sounds like your expansion tank has failed. Baxi usually has a expansion tank built in to the boiler they can be a pain to service. I would just install one on the boiler supply piping.
Your boiler better have a pressure relief valve that should open up after the boiler pressure exceeds 3 bar. If it doesn't shut it down immediately and call for service because it's extremely unsafe to operate.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements