Flue liner
Bob_115
Member Posts: 39
in Oil Heating
Does any one in the USA make a ceramic flue liner like the ones made in Germany by Hart? These liners are light weight ,sturdy and impervious to condensates.
0
Comments
-
Whats the application?
There was an error rendering this rich post.
0 -
This would be used as a liner for the installation of a Biasi B10-3 oil fired boiler. The chimney has an 8X8 clay tile liner.0
-
Wonder why you dont want to use the standard SS liner?
You know you can direct vent that too.There was an error rendering this rich post.
0 -
Just reline with a 316Ti ss listed liner. That ceramic liner is not currently recognized in the US that I can find. You can direct vent that boiler but you can't direct vent it through that ceramic liner, which was designed for negative vent pressure only.0
-
I live in a one story ranch built on a slab foundation. The present boiler is in the middle of the house where the chimney is. The neighbors homes are fairly close and they enjoy sitting in their backyards so I am afraid a direct vent would create a nuisance for them. Do you think this is a realistic view?
As for the ceramic liner I was just exploring my options.0 -
-
Why not use polypropylene? Easier to install and not as expensive.
https://forum.heatinghelp.com/discussion/165045/polypropylene-plastic-chimney-liner-kits-and-their-hard-pipe-for-venting-condensing-equipment8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Polypro has a max. service temp. of 230°F. This boiler is rated at 350°flue gas outlet temp. This is oil fired. Most PP are listed only for CAT IV gas.
0 -
An interior chimney doesnt necessarily need a liner. Less prone to condensation. Just check the terracotta and get a cap.0
-
You need a video camera and training to "check" flue tile. Trust me: I do it for a living. Yes, interior chimneys are less prone to condensation but still they must be suitable for the class of service. That is determined by the building code and an inspection. The IRC points you to NFPA 211 for chimneys serving heaters. Chapter 15 in 211 details what, where, when and how to inspect. Do you really think you can look up or down a chimney and confirm not only are the flue tiles solid with no defects but the mortar in the joints is completely filled joints, struck smooth using a medium duty non-water soluble calcium aluminate refractory cement mixture? That is the Standard of Care along with sizing and height above the roof. Still waiting to find that chimney properly built to code. Haven't met anyone who's found that unicorn either.1
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements