Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!

Startin, stoppin and clickin furnace

Options
Luchie47
Luchie47 Member Posts: 2
The video can explain better than I can. I replaced the nozzle, cleaned the pump filter/screen. I haven't changed the cartridge filter yet as I cant find one local on a sunday. Little over a 1/4 tank of oil.

The problem
https://www.youtube.com/watch?v=84pWJUmV7Wc

I checked for spark
https://www.youtube.com/watch?v=mQdTKnpGt8I

https://www.youtube.com/watch?v=OOUwAkJwN68

Not sure where to go from here. Any help would be appreciated.

Comments

  • Ironman
    Ironman Member Posts: 7,927
    Is the burner motor starting? If so, do you have a gauge that you can attach to the pump or nozzle line to check oil pressure? Is the coupling good?

    You really need to do the filter once you confirm the motor is starting.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Loose/broken wire, or bad relay in one or more of the components.
    Now that you changed your nozzle, did you do a combustion test?

    There was an error rendering this rich post.

  • DZoro
    DZoro Member Posts: 1,048
    Confirm solid thermostat call for heat. If that is good then probably new control.
    D
    rick in Alaska
  • SuperTech
    SuperTech Member Posts: 2,669
    Those three wire primary controls are garbage. Buy a Honeywell R7284U and set it up for interrupted ignition. It might not be the problem, but it will be a great improvement to the boiler.
  • Luchie47
    Luchie47 Member Posts: 2
    Just a quick update, It was indeed the control unit. I appreciate the help! Thank you!
    DZoro