Wiring Ecobee to Burnham boiler
TXBDan
Member Posts: 28
Hello all,
I recently had a Burnham Independence IN5 boiler installed. Here are the installation instructions for reference (Electrical on Page 16):
https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Burnham-SIN5LNI-LE2-Install-Instructions.pdf
I have an Ecobee 4 thermostat that i'd like to install. Here is documentation on that:
https://support.ecobee.com/hc/en-us/articles/227874667-Heat-only-2-wire-boiler-furnace-installations-for-ecobee-thermostats
I currently have only 2 wires running to the tstat to switch the boiler on/off.
I'm fine with running new wire between the tstat and boiler so adding a 3rd wire for a C wire would be fine. I could also run 4 wires which would open up the possibly of running a wall wart power supply.
What options are possible and what do you all think would be best?
Thanks a lot,
Dan
I recently had a Burnham Independence IN5 boiler installed. Here are the installation instructions for reference (Electrical on Page 16):
https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Burnham-SIN5LNI-LE2-Install-Instructions.pdf
I have an Ecobee 4 thermostat that i'd like to install. Here is documentation on that:
https://support.ecobee.com/hc/en-us/articles/227874667-Heat-only-2-wire-boiler-furnace-installations-for-ecobee-thermostats
I currently have only 2 wires running to the tstat to switch the boiler on/off.
I'm fine with running new wire between the tstat and boiler so adding a 3rd wire for a C wire would be fine. I could also run 4 wires which would open up the possibly of running a wall wart power supply.
What options are possible and what do you all think would be best?
Thanks a lot,
Dan
0
Comments
-
You can also add a common wire maker kit on the existing two wires. I have one on my van for these situations. I believe the box says something like "fast stat" on it. If you can wire a relay then you can install the kit.0
-
Your thermostat connection is with Blue and Brown at the boiler. The Yellow wires shown off the other side of the transformer is the Common you need for the EcoBee. It's a 40va transformer so you're good.
Dont add a third wire. Run a new 4 conductor wire and use the existing as a puller. You only need three wires but that fourth might be needed someday.1 -
Ok, that makes sense. I see the yellow is used as C/Neutral/GND elsewhere in the circuit. Thanks!0
-
I wired it up today and its working like a champ. Thanks!0
-
I have the same issue. How did you connect your new C wire to the yellow wire exactly?0
-
I don't remember exactly, but i believe I ran the new 3-wire HVAC wire the same way the old 2-wire went, to a metal junction box above the boiler. I think its where the transformer is. I unscrewed a cover and inside were many wires included the yellow ones. There were two yellow wires wire-nutted together so i added the HVAC C wire to that bundle and it works. I'll double check and take a pic tonight.4lane said:I have the same issue. How did you connect your new C wire to the yellow wire exactly?
0 -
Might I add... don't count on the colour coding of wires being correct. Even licensed electricians make some odd choices, now and then... test and verify.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements