zone valve problem on controller or relay?
Because it will a big job to change the whole controller then I want to make sure it is really the problem of controller rather than the problem on the relay or connections. Thanks in advanced.
I am not sure if I have clearly presented the problem since this is the first time to have this question. If you need any information, I will add them according to your suggestions. Thanks.
Comments
-
I am guessing your 2 thermostats each open their respective control valves. Then the end switches on each valve are wired in parallel and go to T & T on a switching relay to start your 1 circulator. What is the controller your talking about?0
-
You have a point on the connections -- and the wire. Double and triple check to make sure the connections are clean and tight and that the wire is broken or damaged.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Sorry, I am not the professional guy. The controller I talked should be the control valves.EBEBRATT-Ed said:
I am guessing your 2 thermostats each open their respective control valves. Then the end switches on each valve are wired in parallel and go to T & T on a switching relay to start your 1 circulator. What is the controller your talking about?
0 -
Thanks for the information. I have changed the wire then it should not be its problem. The biggest possibility is the connection between wire and replay panel. There is 6 pairs on the panel and Zone 1 and 2 uses two pairs while there is only one line connected to one of the 3rd pair. I am wondering if I can change the connection of Zone 2 to 4 th pair to check if the connection on the 2nd pair is bad. But have no idea how to wire~~~Jamie Hall said:You have a point on the connections -- and the wire. Double and triple check to make sure the connections are clean and tight and that the wire is broken or damaged.
0 -
One interesting is that when I disconnected the wire, there is some spark between wire and screw, then the pump starts running. Then I will tight the screw but it will last one day or maybe 2 days before stop working. However, if there is no spark, the pump doesn't run even the wire is connected~~0
-
-
I have called the electrician came to check but they said everything was well and suggested me to change the whole valve. But I think it is not the problem of valve. Maybe I will call another electrician to check.STEVEusaPA said:Careful with the sparking, you could do damage.
So how long has this been going on, and when are you going to get someone in there (that knows what they are doing) to fix it before you start damaging things?
BTW, the voltage between wire and screw on the pannel should be max. 24 V, am I right?0 -
Which wire, which screw?uqacleo said:
I have called the electrician came to check but they said everything was well and suggested me to change the whole valve. But I think it is not the problem of valve. Maybe I will call another electrician to check.STEVEusaPA said:Careful with the sparking, you could do damage.
So how long has this been going on, and when are you going to get someone in there (that knows what they are doing) to fix it before you start damaging things?
BTW, the voltage between wire and screw on the pannel should be max. 24 V, am I right?
With low voltage it can be a little higher, little lower, just like line voltage.
Maybe instead of an electrician you need a boiler tech familiar with troubleshooting and repairing controls.There was an error rendering this rich post.
0 -
Don't call an Electrician. You need a heating service technician. Google HVAC companies for your area or better yet use the find a contractor tool available on this site.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements