105 ULTRA SERIES 3 HEAT EXCHANGER

Options
Has anyone had experience cleaning the water side of an Ultra heat exchanger. When I arrived at the clients house the boiler was cycling on high temperature with the return pipe cold and the supply line very hot. The boiler is piped secondary to the main loop that seemed to be moving water fine with a very low delta t. The Taco boiler pump on the return line of the boiler had a smoking hot motor even through the piping was cool. I took the Taco pump apart and found it to have a locked cartridge and the impeller was full of blue green deposits. I began flushing the boiler and got more of the blue green stuff. After changing the pump cartridge the boiler still has very large temperature rise. I feel the heat exchanger is partly blocked and feel it needs to be cleaned, but I am not sure how to proceed. Any thoughts???

Comments

  • HVACNUT
    HVACNUT Member Posts: 5,841
    edited February 2019
    Options
    Weil McLain offers Sentinel X-100 inhibitor.
    If you get the maintenance kit, it comes with.
    Also get the HX cleaning tool.
    LES WEGENER
  • Ironman
    Ironman Member Posts: 7,376
    Options
    Fernox boiler cleaner.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    kcoppLES WEGENER