Weil McLain Aqua Plus differential control - tepid to scalding
Hi everyone,
I have a fairly new 80gal Aqua Plus attached to an Evergreen 105 boiler. A recirculation loop is also installed.
https://www.weil-mclain.com/sites/default/files/field-file/WM Aqua Plus Series 2 Water Temperature Controller Instructions 082718.pdfThe differential on this seems to be about 15F. When I set it to 120, I've gotten nearest sink readings from 108 to 120. Raised setpoint to 130 and have seen 112 to 125. Raised again to 135 and see 117 to 132. These are all taken when the tank is not calling.
The instructions don't say that you need to always install a tempering valve. But with this big of a differential, I don't really see how our family can safely use it without one.
80 gallons of water at 108 is not what I'm looking for. Calling for heat when sink drops to 117 seems more appropriate. However, the 132 seems risky to me. We only have adults and teens in our family, but I worry about elderly visitors.
Is this normal for these tanks? Or do people usually see better differential control?
Thanks,
Dave
0 ·
Comments
That said, however, there are some nasties which grow in hot water, particularly Legionella, which you truly don't want. They can't survive water at 140, though, so our recommendation is to set the tank to reach 140. Then, of course, use a mixing valve with thermostatic control to bring the water delivered to the users down to something safe -- 110, perhaps.
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
A mix valve is good insurance. The cash acme ones are simple to install.
https://www.supplyhouse.com/Caleffi-521519AC-3-4-Sweat-MIXCAL-3-way-Thermostatic-Mixing-Valve-w-Temperature-Gauge-Check-Valve