Uponor manifold incorrectly installed. Can I simply reverse the pieces?
a4agarwal
Member Posts: 7
I have a radiant heating system in my home, and I noticed my uponor manifold is installed incorrectly. I have attached a photo below. As you can see, the hot water is going into the return line of the manifold, and the cold water is coming out of the supply side.
Overall the system works, but Uponor said this isn't optimal. Also, the flow meters don't operate at all.
Can I simply swap the two manifold pieces in this situation? The water lines to/from the boiler are copper and can't be moved easily. The red loops don't have any slack in them so I can't move them. But I think I can just swap the placement of the two manifold pieces. Is this right?
Thanks!
Overall the system works, but Uponor said this isn't optimal. Also, the flow meters don't operate at all.
Can I simply swap the two manifold pieces in this situation? The water lines to/from the boiler are copper and can't be moved easily. The red loops don't have any slack in them so I can't move them. But I think I can just swap the placement of the two manifold pieces. Is this right?
Thanks!
0
Comments
-
0 -
You should be able to. Which one is now the supply?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Right now the one on top has the hot water going to it (you can see the red at the top right of the photo)0
-
Having the flow backwards will cause the flow meters not to work as you've discovered. Other than that, probably not an issue. You should have no problem switching them other than purging air which may be minimal if the manifold is higher than the tubing.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
-
The very first radiant system I ever installed was my own back when I was 18 in my 40x40 shop. Used Zurn manifolds, piped it backwards just like yours. It's been that way for 12 years and has never failed to heat the building (in MN, was -35F this morning) with 100 degree supply water. No, the flowmeters don't work but I'm okay with that. Judging by the delta T and pump curve, it's flowing perfectly1
-
I haven't used those manifolds so I could be wrong on this, but it looks like you can remove, and just swap out the flow meters with the flow valves. It looks like the actual manifold of the supply and return are identical.
D0 -
If ever actuators were added, they do not like to work against reverse flow. I'd change it if you can.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements