1/2" fintube?
icy78
icy78 Member Posts: 406
I was at a house last week for low heat and I saw the baseboard loops all piped in 1/2"copper. Just wondering, was/is it common to use 1/2" fintube back ,say 50-60 years go? Or would that go to 3/4" at the fintube? Also the HO said that when they remodeled they removed a loop of bare copper from under the bathtub. I bet that was nice. Pretty highend back then?
The aquastat was set for 150 and it was -4 that morning and they were chilly. Set it at 185 and good so far.
What would the btu rating be on 1/2" fintube compared to 3/4?
  • Intplm.
    Intplm. Member Posts: 3,033
    Was common on monoflo or venturi tee type sytsems back then.
    hot_rod Member Posts: 27,501
    Lower flow rate in smaller diameter fin tube, and shorter zones. They sometimes ran those smaller diameter fin tubes much hotter to get the output required.
  • icy78
    I wondered about that.
    He said his old boiler kept up fine. He just sent me a text and said its still not as warm as before so I may just run it hotter for him. I've no idea what was installed before, or at what temperature.
  • icy78
    I just found Peerless boilers ...The Color of Water.
    I see where the btu rating is almost identical for 1/2 versus 3/4" fintube. Appears the allowable length is less, which makes sense.
    HVACNUT Member Posts: 7,466
    My house, built in '72, purchased in '02 had one zone split loop with all 1/2" baseboard, aluminum wiring, and R7 insulation.
    Immediate renovation/addition. All 3/4 now.
    Funny name too on the baseboard. Mini Might or something like that.
    icy78
    EBEBRATT-Ed Member Posts: 20,228
    Not much difference in the output of 1/2 or 3/4. Most supply house only carry 3/4 and it gets reduced to 1/2 inch pipe when installed
    Some of the older books recommended 200-210 deg water. Things are different now. Lower water temp saves fuel.
    I usually go with 190 limit with a 20 deg TD gives you a 180 average water temperature
    icy78