Baseboards not getting warm
rx7145
Member Posts: 7
I’m having problems with some of my baseboards not getting hot.
I’m in the process of installing some zone valves in my system to separate the upstairs, downstairs and a radiant floor zone. During the install of the valves I must have gotten some air in the system as the baseboards in the basement that run off zone B are not getting hot. I have bled them multiple times and every hooked up a hose to “power flush” the system which seemed to help for a little while but they went clod a short time later.
This is a mono-flow system with the main line 1” and the runners 3/4. I’m wondering if the old (65’) balance valves could be my problem? I’m including some pictures and a diagram of my system.
Thanks for any help.
https://photos.app.goo.gl/7mnVeyxvDJnR84446
I’m in the process of installing some zone valves in my system to separate the upstairs, downstairs and a radiant floor zone. During the install of the valves I must have gotten some air in the system as the baseboards in the basement that run off zone B are not getting hot. I have bled them multiple times and every hooked up a hose to “power flush” the system which seemed to help for a little while but they went clod a short time later.
This is a mono-flow system with the main line 1” and the runners 3/4. I’m wondering if the old (65’) balance valves could be my problem? I’m including some pictures and a diagram of my system.
Thanks for any help.
https://photos.app.goo.gl/7mnVeyxvDJnR84446
0
Comments
-
I’ve been jammed on that, you have air somewhere. You could hook up a fire engine to purge and it won’t work. Just look at the system and think if you were air, wheee would you hide. You bled all the bb units? Sometimes the bb will sag the wrong way0
-
On the monoflo loop, did you bleed the rads themselves?
Bleeding the rads can be a pain. Try raising the pressure to 25 psi and bleed. It helps with 2 people. 1 to bleed, 1 to keep the pressure up. Set back to 12 psi when done.
Did you alter the monoflo loop at all? That's a whole different story. If so, you'll need to show what was done.1 -
> @HVACNUT said:
> On the monoflo loop, did you bleed the rads themselves?
> Bleeding the rads can be a pain. Try raising the pressure to 25 psi and bleed. It helps with 2 people. 1 to bleed, 1 to keep the pressure up. Set back to 12 psi when done.
> Did you alter the monoflo loop at all? That's a whole different story. If so, you'll need to show what was done.
I added the zone valves. (See pictures) I’ll take some better ones as well soon.
I have blead the baseboards many times. There are bleeders in the ceiling. I’ll take a picture of them as well.0 -
rx, I saw the pics, there's a lot going on there. Those crusty valves near that threaded steel piping- that could be some of the trouble. One needs to 'force' water into every single piping route. If the zones are 'split', then we need to isolate the splits and get each section purged.
0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements