B&G redfox - corrosion?
This is only 4 years old. Any ideas?
    Jamie Hall Member Posts: 27,577
    Find out where the moisture is coming from that's getting on it -- before it ruins the pump.
    CanuckerMiketheNewbieHomeowner
    hot_rod Member Posts: 27,824
    A leak above dripping on it? Or water running down one of the wire conduits?
  • kcopp
    kcopp Member Posts: 4,699
    What is the system material piping like?
  • Here’s a better view of setup - I probably should have mentioned, this feeds a built-in wall heater fan, which operates as its own zone (kitchen).
  • EzzyT
    EzzyT Member Posts: 1,380
    edited January 2019
    That’s the wrong circulating pump for that application, the circulating pump needs to be a 3 piece bronze oil lubricated pump. That is going fail.
    Plus the tapping that’s used as the supply is way to high it needs to be at the return piping or at the boiler drain tapping. Boiler needs to be skimmed too.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
    CanuckerkcoppMiketheNewbieHomeowner
  • kcopp
    Ditto.
  • KC_Jones
    KC_Jones Member Posts: 5,939
    Steam piping appears to be incorrect as well.
    2014 Weil Mclain EG-40
  • JUGHNE
    JUGHNE Member Posts: 11,603
    Does anyone see the "steam drier/drum/chamber" on the outlet of the boiler. I am guessing that is what it is. Were they effective?
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,728
    Steam separator. Yes, they’re effective. And ditto on the circulator.
    Retired and loving it.
  • Thank you all for the quick insight and great help! Will do some further digging and report progress.
    Are we talking the $789 B&G bronze 3 pc pump here? If so, Any alternatives come to mind?
  • I'm not sure how this application would cause the rusting between the electrical box and stator housing. The only things I'm aware of that can cause this are:
    - Moisture following along the electrical wire as Hot Rod says, getting into the electrical box
    - Condensation building up in the stator (between the rotor can and stator housing). This is more typical in chilled water applications where the water temp is lower than ambient causing windings to sweat (obviously not in this situation)
    - A hole in the rotor can
    Clearly this needs to be addressed - if the stator and electrical box flood you will release the magic smoke. Kidding aside, this circ is doomed to eventually fail, either from the excessive moisture in the wrong area or by the misapplication (wet rotor circs do not like the somewhat abnormal TDS and PH typical found in boiler condensate).
    Agree a 3 piece mechanically sealed circ is a better selection (and replacing seals is much cheaper than the complete circ or it's cartridge).
  • KC_Jones
    Replace that style pump every few years is the alternative.