Radiant system pump selection

cbarner69
Member Posts: 2
I am trying to determine if my pump is sized correctly. I have an in slab system, 1/2” per 12” spacing. Each loop is 300’ with 8 loops. I am using a Rhani on demand water heater. The delta t is approx 70 deg F. Flow rate per loop is .4 gpm. I purchased 2 Taco 007-f5 pumps. One on the supply and one on the return.
I am thinking the pumps are too small to provide the proper flow to get a better delta T.
Inlet temp is 140 F outlet temp is 70 F.
I am thinking the pumps are too small to provide the proper flow to get a better delta T.
Inlet temp is 140 F outlet temp is 70 F.
0
Comments
-
We get at least one of these a week.
The 007 would work just fine if you were piped primary/secondary as you should be.
Hot water heaters are not boilers and will not last very long or perform very well in that application.
If you post pictures and drawing, you will get more detailed advice."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
That's 112,000 BTU per hour dumped into the space which I can only assume is roughly 2400 sq ft. Is this space missing a wall or did someone forget to insulate? Your flow rate is actually pretty decent judging by the flow rate (if accurate) which would likely be raised a bit by P/S piping as the head loss through a tankless is stupid high. As for your delta, I'd be willing to bet if you turned the supply temp down to 100 or so, your delta would cut down to about 25 degrees and would run longer for a more even heat. That's just speculation of course, without some details on the building0
-
The building is 2400 sq ft with 14 ft ceiling. I insulated the ceiling but need to do the walls. I want to do spray foam insulation on the walls but have to wait for warmer weather. I will try the lower temp and see how that works.0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements