Looking for a Quieter Boiler
I just refinished my basement and am looking for some input. I currently have a 25 year old, Weil Mclain HE II boiler that's just a little louder than I would prefer. Unfortunately, because of it's location, the boiler needs to be atmospheric vent. Does anyone have any experience with the Burnham models (ES2, series 2, series 3), Peerless MI series, or Weil Mclain CGA series and can attest to their sound levels? Any input would be helpful. Thanks
Comments
-
Any atmosepheric natural draft boiler should be quiet; it's the ones with inducers that are louder.
You can stand next to an ES2 and not know its firing.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Thanks Ironman. That's exactly what I was hoping to hear as I really like the ES2 model.0
-
-
> @Solid_Fuel_Man said:
> System 2000. The quietest oil boilers I know of.
He's got gas but the System 2000 might be even more quiet with the EZ Gas.
And tons more efficient than an atmospheric boiler.1 -
agreed, let's outlaw atmospheric OK???? it's 1940"s technology and about 40% efficientHVACNUT said:> @Solid_Fuel_Man said:
> System 2000. The quietest oil boilers I know of.
He's got gas but the System 2000 might be even more quiet with the EZ Gas.
And tons more efficient than an atmospheric boiler.0 -
-
Thanks for the input. Unfortunately, because of the boiler location, the only place I am able to vent is through the chimney, thus requiring me to use at atmospheric vented boiler. I would love to use something else, but I just don't see how. And I should have clarified the the fuel source is Natural Gas.0
-
-
I had thought about something like that but I also have the hot water heater venting through the chimney as well. So I would need to take that into account also. Right now the boiler and HWH are tied into the same vent pipe.0
-
that doesn't require you to use atmospheric, the chimney can be used as a chase for PVC or lined for a System 2000Mudaero said:Thanks for the input. Unfortunately, because of the boiler location, the only place I am able to vent is through the chimney, thus requiring me to use at atmospheric vented boiler. I would love to use something else, but I just don't see how. And I should have clarified the the fuel source is Natural Gas.
1 -
You could use an indirect water heater with a mod/con. They come already setup for the addition of one. You'd have a lot more hot water, too.Mudaero said:I had thought about something like that but I also have the hot water heater venting through the chimney as well. So I would need to take that into account also. Right now the boiler and HWH are tied into the same vent pipe.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.3 -
The system 2000 will include a brazed plate heat exchanger and hot water tank. It will provide you with endless amounts of hot water and make it using less energy than your current setup.0
-
Creates a little larger investment than I was hoping, but it's definitely something to consider. I assume the direct vent boilers are quieter than the atmospheric ones?0
-
^ direct vent and power vent both have blowers which atmospheric boilers don't have... it can be a source of noise.
A properly sized mod-con boiler spends most of it's life firing at a very low rate however, so the blower is also running at a very low RPM which helps keep noise down. When firing on low, I have to actually look at the panel of my mod-con to see if the flame is on (vs. just circulating warm water without adding heat)- that's how quiet it is running on low fire.4 -
HE II, that's what Dad had put in the family home just before moving. You ain't a kidding that thing is loud. I've heard oil burners lots quieter. We've sold some Series 3, just a whisper.0
-
Good to get some perspective from someone who knows the current sound level I am dealing with. Never really bothered me when the basement was just a basement. But now as a finished area, I would really like to reduce the noise as much as I can.0
-
A mod/con with indirect is my vote. Absolute quietest for gas.
What type of radiation do you have? Cast iron, baseboard etc?Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
Actually, that's another good point to mention, it's actually a mixed system. Basement is slant/fin, all others are cast iron. 2 zone valves separate the systems. I feel the basement calls for heat more often (it is really well insulated) but the baseboards won't hold the heat like the radiators. This would be another reason why a constant cycle at a low fire rate would make sense (as stated above).0
-
If you are or have finished off the basement don't forget about combustion air. See too many folks just wall off the mechanical room and the unit starts sooting, CO and poor performance....0
-
No issue with combustion air. The mechanical room is very small but there is a full louvered door so it gets plenty of air flow. Coincidentally, this is one of the reasons I am looking for a new boiler as a full door would have been quieter but the air flow would not have been there.0
-
Mod-cons love cast iron... it virtually eliminates short-cycling.Mudaero said:..it's actually a mixed system. Basement is slant/fin, all others are cast iron. 2 zone valves separate the systems.
Please measure the lengths of the actual fin tube elements inside the slant/fin enclosures and add them together, we can then see how much heat that zone can radiate.
Is the cast iron baseboard or conventional radiators?
0 -
18' of Slant/Fin (Multi Pak 80, 730 BTU / Foot @ 180°). The rads upstairs are classic cast iron. 4 on main floor (estimated @ about 40,000 BTU max) and 3 upstairs (estimated @ about 20,000 BTU max).0
-
Strike that, the Multi/Pak 80 comes in at 840 BTU @ 4 GPM @ 180°0
-
You need to use 170* AVERAGE water temp to calculate the output.Mudaero said:Strike that, the Multi/Pak 80 comes in at 840 BTU @ 4 GPM @ 180°
But regardless, there may not be enough of a load from that to preventing short cycling of a low mass mod/con. You need to compare that number to the minimum firing rate of whatever model and size mod/con is selected to determine if some buffer or combining of zones will be necessary.
The HTP UFT boiler has a 10 to 1 turn down, so an 80k btu would have a minimum firing rate of 8k btus. A lot of mod/cons only have a 5 to 1 turn down.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
Weil Mclain ultra oil, it's a cast iron boiler that will last much longer than a system 2000.0
-
> @ChaseNP said:
> Weil Mclain ultra oil, it's a cast iron boiler that will last much longer than a system 2000.
The OP is looking for a quiet gas boiler, not oil.
The Ultra oil is an ok boiler when using a Beckett NX burner but its not exactly quiet. I've never seen one with a gas conversion burner but I'm sure they're out there.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements