Pressuretrol Not working
So my pressuretrol was not working. Pressure kept going up. So i bought a new pressuretrol and that also does not seem to be working. Is it possible that the new pressuretrol is bad? I did try to save some money by buying it from ebay.
Should i return it and buy from a reputed source or problem could be something else?
I do have Pressuretrol after the pigtail and i have the low pressure guage on the same line connected on the Tee. So it is not the clogged pigtail
Please help.
This is the pressuretrol on the boiler.
PA404A 1009 2
I think it's much more likely that the wiring is incorrect and the pressuretrol (new and old) isn't in the control loop. How long was the old one being ignored? Did it ever work as seen by your eye?
From far away, I still doubt the pigtail if you haven't actually blown through it. Is your low pressure gauge moving from 0 during a call for heat and then getting pegged at the top and then lowering back down after firing ends?
Or maybe both ptrolls are set incorrectly? What is the highest pressure you have seen? Did it make the pressure relief valve blow?NJ Steam Homeowner.
Can you send a photo of the front of it?
You can help rule out the incorrect wiring by disconnecting one terminal in the pressure troll to see if your boiler will still fire in that state. If it does, then the system wiring is borked and is ignoring the pressuretrol.NJ Steam Homeowner.
I will try disconnecting one terminal.ethicalpaul said:Can you send a photo of the front of it?
Does it matter which terminal goes where?0 -
No, it's a simple switch so it shouldn't matter which wire goes on which terminal.kevinjames79 said:
No, the pressuretrol is just a switch so it doesn't matter which wire is on which terminal, if that's what you're asking.
Other than disconnecting the terminal, is there any other way to test the pressuretrol?KC_Jones said:
Take it off, clean the nut, put your mouth on it and blow. If you hear a tick on and off, it's working.
Make sure the differential is 1 and 1.5 on the dial.0 -
Disconnecting the terminal doesn't test the pressuretrol, it is to prove if your boiler isn't listening to the pressuretrol.kevinjames79 said:
The pressuretrol might still be bad or good if this test fails, but you'll know to stop chasing the pressuretrol as a cause because your other wiring is not good if the boiler keeps running with the pressuretrol disconnectedNJ Steam Homeowner.
I just tried to blow the old pressuretrol and i do not hear anything.
I will disconnect the new pressuretrol tonight and will try the same test on that one.
Now.. just for the sake of info.... if i do need new pressuretrol, which one do you guys recommend?0 -
I'm really curious now...how hard did you blow and what is the setting of the device currently?
I did blow really hard. The cutoff differential was set at 1. The new device is also set at 1 differential.0
That’s good. And the cut in setting on the front is all the way down?
@kevinjames79 when you changed these Pressuretrols, did you also take the pigtail (looped pipe that the Pressuretrol is mounted on) off and clean it out. It sounds like it is clogged to me and no Pressuretrol will work if that's the case. It could be clogged past the Tee that your gauge is attached to.1
Fred... It was clear as of 3 days ago when i changed it.
I am going to check again any way. But worst case scenario.. should i get new pressuretrol if nothing works out?
If yes, then which one?0 -
@kevinjames79 , it is not likely that two Pressuretrols have failed. Double check that the wires are connected at both ends and that the wire isn't broken.
The one you want is a PA404A 1033
Before you order a new one, take the cover off and make sure that when you set the Cut-In to .5PSI that you did not turn it too much and the spring linkage behind the Cut-In did not drop off of the end of the screw. If it did, re attach the linkage.
Those Pressuretrols almost all need to be re-calibrated right out of the box. They are typically off by 2 or more PSI.
Here is the procedure to recalibrate:
Inside the Pressuretrol, right below the micro switch, there is a pivot arm. At the end of that arm you will see a screw pin that is activated by the diaphragm at the bottom of the Pressuretrol. If you look very carefully at that screw pin, you will see it actually has a tiny (I mean tiny) hex head on it. It takes a .050 hex wrench and you can turn it clockwise (Towards the bottom of the Pressuretrol to decrease the Cut-out pressure or counter clockwise to increase the cut-out pressure (which none of us want to do but who knows, your Pressuretrol may be really screwed up!). Turn the power to the unit off first. You may find the first attempt to turn that screw a little bit stubborn (relatively speaking) because it has some Locktite on it but it does turn. Don't turn too much, a fraction of a turn goes a long way towards getting it adjusted where you want it (maybe 1/32 inch turn to start with). You may need to play with it to get it exactly where you want cut out to be.1 -
Awesome tip. I will try it out. First i need that damn small hex wrench.
Thanks0
- 87.8K THE MAIN WALL
- 129 Chimneys & Flues
