Grundfos 26-64 pump opening Honeywell zone valve.
Alan (California Radiant) Forbes
Member Posts: 4,243
I have a customer who says that his master bedroom zone overheats. The room continues to heat when the thermostat and zone valve are off and one of the other zones is on. The Honeywell zone valve operator was replaced by another contractor which didn't help and I almost replaced the valve today until I decided to check his system pump which is a Grundfos 26-64 which I believe is oversized and could be forcing the zone valve to slightly open, heating the space. This overheating happens only in the master bedroom zone which is furthest away from the pump. If I manually open and close the zone valve at the lever on the operator, it feels fine.
At this point, I don't know whether to replace the pump or the zone valve.
Honeywell spec's.: https://forwardthinking.honeywellhome.com/related_links/water/5000_series/install/95c_10932.pdf
Grundfos spec's:
https://product-selection.grundfos.com/product-detail.product-detail.html?custid=GMA&lang=USA&productnumber=52722330&qcid=471285683
Flowing 8 gpm @ 6' head.
At this point, I don't know whether to replace the pump or the zone valve.
Honeywell spec's.: https://forwardthinking.honeywellhome.com/related_links/water/5000_series/install/95c_10932.pdf
Grundfos spec's:
https://product-selection.grundfos.com/product-detail.product-detail.html?custid=GMA&lang=USA&productnumber=52722330&qcid=471285683
Flowing 8 gpm @ 6' head.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab
Two btu per sq ft for degree difference for a slab
0
Comments
-
I had one of those Honeywell zone valves with the rubber ball plug that closes the valve off. On mine the ball had deteriorated to the point where there wasn't much of it left and it was doing nothing to stop the flow of water past it even when closed.
0 -
Have you ruled out gravity flow? Are the zone valves on the supply or return? Do you have any pictures of the piping?0
-
You might need both. I agree that the pump is oversized. Has it trashed the valve?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
that is a very low shutoff pressure on the high Cv valve? Typically a 20 psi shutoff for large Cv, up to 75 psi on smaller Cv valves. No doubt even a 15-58 could push open that valve.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements