Main burner not igniting

My pilot light is lit. I have 24v at the gas valve. Would I be getting power at the valve if the limit switches were bad?

Comments

  • HVACNUT
    HVACNUT Member Posts: 3,906
    The short answer is no way Jose'.
    All safeties and limits should be in series before the gas valve.
    You've got 24v so you're looking at a bad valve or a gas pressure issue.
    Do you have a manometer?
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 8,823
    @jakeaarongarner

    just make sure you are on the right gas valve terminals with the meter. Sounds like a bad gas valve
  • Tim McElwain
    Tim McElwain Member Posts: 4,451
    What is the Make and number of the valve?