Taco Zone valve troubleshooting. Heating issue...*
Shachar
Member Posts: 36
in Gas Heating
Hi,
Sorry if this discussion is showing twice. I posted this question, then after posting the table I created did not show up properly, so I edited it and saved, but then the discussion disappeared. If the previous one shows up, I'll delete/close it to avoid duplicating of it.
I tried searching the forums, and searched google for answers, but didn't find an clear explanation of the following:
I have hot gas/water baseboards for heating, 2 zones, and Taco valves.
Heating for zone 1 does not work properly. Seems that during the day it's not heating at all and zone1 temp is around 63F even if I set the thermostat to 69 or 70.
At night the temp in zone 1 is about 68. outside it's actually colder (24F) so I don't know what's going on.
Trying to troubleshoot this to see if my zone1 valve is defective, or maybe the transformer or the wires.
I tested with voltage meter and these are the readings:
---------------------------------------------------
Thermostat ON Thermostat OFF
---------------------------------------------------
Screws 1&2 2&3 1&2 2&3
---------------------------------------------------
Zone1 21.4V* 25V 0 25.1V
---------------------------------------------------
Zone2 24.4V 0 0 25V
---------------------------------------------------
Transformer:
Zone1Only 22.5V 24.5V
Zone2Only 22.5V-24.5V 24.5V
---------------------------------------------------
Valve
When Zone2 Thermostat is ON then Zone2 manual Valve opens all the way if I pull it.
When Zone1 Thermostat is ON then Zone1 manual Valve goes up just a quarter of the way if I pull it.
*Another time I tested Zone1 with Thermostat ON Voltage was 19.4V-21.1V
Note: When Zone2 Thermostat ON then Zone1 2&3 showing 0 volt. Tested this twice.
Thermostat for Zone1- tested wall wires = 24.5V. Tested Thermostat itself for continuity when ON = YES, when OFF = NO continuity.
Can anyone please help shed light on what is going on?
I got a new Taco zone valve from the store, but I want to understand all this before attempting to install it to see if it resolves the problem.
I can attach pictures of the transformer and the valves, but I believe this is enough info.
Thanks,
Shachar
Sorry if this discussion is showing twice. I posted this question, then after posting the table I created did not show up properly, so I edited it and saved, but then the discussion disappeared. If the previous one shows up, I'll delete/close it to avoid duplicating of it.
I tried searching the forums, and searched google for answers, but didn't find an clear explanation of the following:
I have hot gas/water baseboards for heating, 2 zones, and Taco valves.
Heating for zone 1 does not work properly. Seems that during the day it's not heating at all and zone1 temp is around 63F even if I set the thermostat to 69 or 70.
At night the temp in zone 1 is about 68. outside it's actually colder (24F) so I don't know what's going on.
Trying to troubleshoot this to see if my zone1 valve is defective, or maybe the transformer or the wires.
I tested with voltage meter and these are the readings:
---------------------------------------------------
Thermostat ON Thermostat OFF
---------------------------------------------------
Screws 1&2 2&3 1&2 2&3
---------------------------------------------------
Zone1 21.4V* 25V 0 25.1V
---------------------------------------------------
Zone2 24.4V 0 0 25V
---------------------------------------------------
Transformer:
Zone1Only 22.5V 24.5V
Zone2Only 22.5V-24.5V 24.5V
---------------------------------------------------
Valve
When Zone2 Thermostat is ON then Zone2 manual Valve opens all the way if I pull it.
When Zone1 Thermostat is ON then Zone1 manual Valve goes up just a quarter of the way if I pull it.
*Another time I tested Zone1 with Thermostat ON Voltage was 19.4V-21.1V
Note: When Zone2 Thermostat ON then Zone1 2&3 showing 0 volt. Tested this twice.
Thermostat for Zone1- tested wall wires = 24.5V. Tested Thermostat itself for continuity when ON = YES, when OFF = NO continuity.
Can anyone please help shed light on what is going on?
I got a new Taco zone valve from the store, but I want to understand all this before attempting to install it to see if it resolves the problem.
I can attach pictures of the transformer and the valves, but I believe this is enough info.
Thanks,
Shachar
0
Comments
-
-
Shachar, phone # is 401-942-80000
-
-
Thanks SteveSan. I called and talked to Ben from tech support. I explained the issue over the phone. He said that most likely I have air in the system for zone 1 that doesn't work and I should try to purge the air out of the system. Was that your reasoning too...?
According to him the voltage readings are fine and the Taco zone valve will open for any voltage over 19 point something (don't remember exactly what he said).
I'll try to purge and see if there is any difference.0 -
Ben is correct Shachar, sounds like you have an air issue and all of your readings are correct. Valve only needs 19 volts to open.0
-
-
Thanks all for the useful suggestions.
I did manually opened the zone1 valve while the thermostat was ON and it did start to heat properly.
I then replaced the valve with a new one I got from the store ($75) and tested again, and it works now. So I guess it was a bad zone valve. I did notice that for screws 1&2 when it thermostat is on there is about ~22V until the valve fully opens and the heating starts, then it's ~24V+ - why is that?
Anyway, thanks again for the help in troubleshooting. The wife is happy now
0 -
once The valve opens, and the heater that opens the valve is disengaged, the amperage applied to the valve goes down, so voltage goes up. Once it needs the heater back on, amperage goes up, so voltage goes down. Only usually have 40 va....use it wisely 😁0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 59 Pipe Deterioration
- 921 Plumbing
- 6.1K Radiant Heating
- 374 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 40 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements