CG400 tied to an old MM Feeder, glitch

GW
GW Member Posts: 4,832
Hey all i'm perplexed, changed a boiler today, told the gentleman i would connect to the existing old school 24v feeder.

I set up a relay and a trans, in order to separate the lwco from the old feeder- I don't want the boiler sending power to the old dog.

Inside the CG400 I grabbed 2 and A for the relay. It's a RIB, I love the tiny light bulb.

The issue is the lwco won't drop out the A when the water level has been met/re-filled. The light on the CG400 does indeed go out, but the RIB light stays on (getting power from A) and the boiler overfills by a large margin.

Thanks for any tips. I did the same thing a few years ago--I didn't really any glitches. Although, that job 3 years ago was a 110v feeder, and this one is a 24v feeder. That doesn't matter anyway, it's still a RIB on both jobs.

Gary Wilson
Wilson Services, Inc
Northampton, MA
gary@wilsonph.com

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,485
    Don't know. Hydrolevel says not to use a solenoid type feeder why I don't know. Plus you have it isolated it with a RIB. Seems like it should work.

    Just thinking out loud your 24 v comes from 2 common and A hot to the coil of the RIB which would be yellow/white common and blue/white hot. I am sure you have the black/white coil wire taped up.

    The 1 leg of your 24v runs through yellow and orange contacts to the feeder.

    I am sure it would be worth a phone call to Hydrolevel.

    Boiler grounded?
  • GW
    GW Member Posts: 4,832
    Yes to all of that, RIBs are the bees knees. I don’t remember the wire coloring very well (yes I have two wires capped off independently). But I’m quite positive it’s wired properly. I’ll give Hydrolevel a buzz tomorrow unless anyone else can chime in
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • Steamhead
    Steamhead Member Posts: 17,387
    It'll never work that way. Problem is, probe LWCOs have a delay when they sense water after a low-water shutdown, to verify that the water isn't going away. Also, when you power up a probe LWCO, it self-tests, which energizes the feeder terminal.

    There are two solutions:

    1- install a delay-on relay between the LWCO and the feeder, setting the delay for at least 30 seconds, or

    2- replace the feeder with a VXT.

    I prefer the latter, because the VXT has the digital display that tells how many times it has fed water.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • GW
    GW Member Posts: 4,832
    Ok but it’s the overfill that’s getting me.
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • Steamhead
    Steamhead Member Posts: 17,387
    edited December 2018
    That's what's causing the overfill. You need to delay the feeder coming on to avoid it.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • GW
    GW Member Posts: 4,832
    i'll give that a try
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA