Hey all i'm perplexed, changed a boiler today, told the gentleman i would connect to the existing old school 24v feeder.
I set up a relay and a trans, in order to separate the lwco from the old feeder- I don't want the boiler sending power to the old dog.
Inside the CG400 I grabbed 2 and A for the relay. It's a RIB, I love the tiny light bulb.
The issue is the lwco won't drop out the A when the water level has been met/re-filled. The light on the CG400 does indeed go out, but the RIB light stays on (getting power from A) and the boiler overfills by a large margin.
Thanks for any tips. I did the same thing a few years ago--I didn't really any glitches. Although, that job 3 years ago was a 110v feeder, and this one is a 24v feeder. That doesn't matter anyway, it's still a RIB on both jobs.
I set up a relay and a trans, in order to separate the lwco from the old feeder- I don't want the boiler sending power to the old dog.
Inside the CG400 I grabbed 2 and A for the relay. It's a RIB, I love the tiny light bulb.
The issue is the lwco won't drop out the A when the water level has been met/re-filled. The light on the CG400 does indeed go out, but the RIB light stays on (getting power from A) and the boiler overfills by a large margin.
Thanks for any tips. I did the same thing a few years ago--I didn't really any glitches. Although, that job 3 years ago was a 110v feeder, and this one is a 24v feeder. That doesn't matter anyway, it's still a RIB on both jobs.
0
Comments
-
Don't know. Hydrolevel says not to use a solenoid type feeder why I don't know. Plus you have it isolated it with a RIB. Seems like it should work.
Just thinking out loud your 24 v comes from 2 common and A hot to the coil of the RIB which would be yellow/white common and blue/white hot. I am sure you have the black/white coil wire taped up.
The 1 leg of your 24v runs through yellow and orange contacts to the feeder.
I am sure it would be worth a phone call to Hydrolevel.
Boiler grounded?0 -
Yes to all of that, RIBs are the bees knees. I don’t remember the wire coloring very well (yes I have two wires capped off independently). But I’m quite positive it’s wired properly. I’ll give Hydrolevel a buzz tomorrow unless anyone else can chime in0
-
It'll never work that way. Problem is, probe LWCOs have a delay when they sense water after a low-water shutdown, to verify that the water isn't going away. Also, when you power up a probe LWCO, it self-tests, which energizes the feeder terminal.
There are two solutions:
1- install a delay-on relay between the LWCO and the feeder, setting the delay for at least 30 seconds, or
2- replace the feeder with a VXT.
I prefer the latter, because the VXT has the digital display that tells how many times it has fed water.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Ok but it’s the overfill that’s getting me.0
-
That's what's causing the overfill. You need to delay the feeder coming on to avoid it.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Categories
- All Categories
- 85.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 424 Carbon Monoxide Awareness
- 73 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 130 Geothermal
- 160 Indoor-Air Quality
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 885 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 59 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements