I’m brand new to both home ownership and understanding all things heat so I appreciate the help.
We got a new steam boiler installed and off the boiler is a forced hot water radiator in a section of the house that was an addition.
These radiators are getting hot as heck and the room isn’t heating consistently. There is one of these https://www.supplyhouse.com/Honeywell-L4006A1678-High-or-Low-Limit-Aquastat-100-240-F-range-5-F-to-30-F-Differential between the boilers and the pump (I think it’s the pump). I’m wondering if I need to change the water temperature in that or change the differential?
We’ve got the thermostat set at 67-68 and the room still get sweltering seemingly after it initially kicks on.
Here is a picture of the whole setup on the boiler: https://i.imgur.com/iiQNCNf_d.jpg?maxwidth=640&shape=thumb&fidelity=medium
As an aside the radiators and hot water copper are rattling and banging, I assume I just need to purge the air to fix that?
We got a new steam boiler installed and off the boiler is a forced hot water radiator in a section of the house that was an addition.
These radiators are getting hot as heck and the room isn’t heating consistently. There is one of these https://www.supplyhouse.com/Honeywell-L4006A1678-High-or-Low-Limit-Aquastat-100-240-F-range-5-F-to-30-F-Differential between the boilers and the pump (I think it’s the pump). I’m wondering if I need to change the water temperature in that or change the differential?
We’ve got the thermostat set at 67-68 and the room still get sweltering seemingly after it initially kicks on.
Here is a picture of the whole setup on the boiler: https://i.imgur.com/iiQNCNf_d.jpg?maxwidth=640&shape=thumb&fidelity=medium
As an aside the radiators and hot water copper are rattling and banging, I assume I just need to purge the air to fix that?
0
Comments
-
The water supplying the radiators is too hot. I don’t see how the aquastat could actually sense temperature properly.
The noises could be air, but more likely rapid expansion.
I assume you had no luck with the installer and he isn’t coming back?There was an error rendering this rich post.
0 -
I could ask him back I was just trying to see if it was a simple tweak to a setting.0
-
Actually there is a fairly simple tweak, but it will involve some plumbing. What is happening is that the boiler is making steam -- so the water which is being used in the hot water loop is way too hot. What is needed is a mixing valve which will allow some of the return water from the hot water loop to be pulled into the supply, rather than having it all go back to the boiler. This could either be manual, or there are thermostatically controlled valves which could be set for a more reasonable temperature.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements