Hot water baseboard system

JimGloseJimGlose Posts: 3Member
Hot water baseboard system, 5 zones
In two of the zones, when the thermostat calls for heat, the valve opens, but the circulator doesn't come on.
Where is the problem?

Comments

  • Jamie HallJamie Hall Posts: 8,945Member
    Check all your wiring and the end switches on the valves for starters.
    Jamie



    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.



    Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • delta Tdelta T Posts: 689Member
    most likely bad end switches. Are these honeywell zone valves? depending on how old they are, you can most likely change out the head without draining any water.
  • JimGloseJimGlose Posts: 3Member
    Thanks fellas!