High Delta T
NeedHvacHelp
Member Posts: 5
Hi,
It's been a cold Thanksgiving weekend. No heat since Wednesday night. I couldn't figure out why it constantly getting high delta T (lockout code 14) and occasionally lockout code 4. Have someone came by and diagnosed bad boiler pump. I have replaced a new pump yesterday evening but still getting lockout code 17. Boiler seems to run fine, though return temp can go only as high as 90 F. We live about 20 miles west of Boston and the house is a little bit under 3000 square feet; Burnham Alpine ALP150W with HTP Superstor 45 gal. indirect heater, 3 zones.
I am sorry my message is a little bit cryptic since I am an immigrant and had very little back home so kind of mechanical challenged. Any help will be appreciated.
KC
It's been a cold Thanksgiving weekend. No heat since Wednesday night. I couldn't figure out why it constantly getting high delta T (lockout code 14) and occasionally lockout code 4. Have someone came by and diagnosed bad boiler pump. I have replaced a new pump yesterday evening but still getting lockout code 17. Boiler seems to run fine, though return temp can go only as high as 90 F. We live about 20 miles west of Boston and the house is a little bit under 3000 square feet; Burnham Alpine ALP150W with HTP Superstor 45 gal. indirect heater, 3 zones.
I am sorry my message is a little bit cryptic since I am an immigrant and had very little back home so kind of mechanical challenged. Any help will be appreciated.
KC
0
Comments
-
Can you post a picture of the boiler and any pumps or zone valves0
-
17 is fan speed not proved
https://www.manualslib.com/manual/689025/Burnham-Alpine.html?page=115#manual
4 is supply high limit temps in excess of 210 degrees
https://www.manualslib.com/manual/689025/Burnham-Alpine.html?page=116#manual0 -
Thank you Leon82. My mistake. It was soft locked out code 14 (Delta T inlet/outlet high). I did see 17 but it would clear itself. 14 is constant and the boiler would go into standby delay with red screen.0
-
Sounds as though the water is traveling too slowly through the boiler, unable to pick up all the heat from the heat exchanger.
Required flow for your boiler is 9.2 gpm at 6.6 ft. head which a small pump can do easily. Now that you've ruled out the pump, I'd say that there's air somewhere in the system, preventing flow.
Do you have radiant heating in the floor or radiators? What is system water pressure?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Make sure the pump is pumping in the right direction .0
-
Alan and Leon82 thank you very much for the info.
Water pressure is 20 psi. The house has three zones. First floor has an ADP hydro air handler, basement has 50 linear feet baseboard and second floor also has a hydro air handler but I am not sure the brand.
I will double check the pump I put in - I believe it was the same direction as the old one I took out.
KC0 -
Boiler pump direction is correct. Finally got heat for about a couple hours. High delta T showed up again.0
-
Searched the forum for delta T issue. Mine seems like “Lochinvar WHN085” that has a faulty sensor of sort.0
-
Maybe unplug it and inspect the connection, the manual may have some values you can check with a multimeter also0
-
Solo 110, 01/4/22. 16.58 days ago, cold snap, I got a Delta T lockout. I have not accessed this before, just hit ok and it started up. Yesterday about 8pm I got the lock out after 4 previous warnings, the most recent was 32 hrs ago. Of course I wasnt aware until at 430 this am that most likely the furnace was down. Sure enough delta t inlet vs outlet temps. What do you trouble shoot to the cause? Temp was 4deg outside. Inside when I realized, was 65. Running as soon as i said ok0
-
Is your boiler piped primary/secondary? What does the boiler say the supply and return temps are? If you feel the pipes do those temps seem about right? Does it sound like you have air in the system?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Snap some pics with your phone or digital camera and show us what you have.
It sounds like not enough flow in the boiler.
Improper piping, wrong pump, clogged strainer, valve not fully open.
If not those it could be a sensor error.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements