Boiler cycling

My boiler in a 2 story house runs for 90 seconds then cycles off for 6-7 minutes. Outside temp is about 30. New Honeywell tstat set for .08 steam. Can this be a problem for my boiler, overuse etc. What will happen when it gets cold in Jan. or Feb. With old tstat, boiler ran for 7 minutes and cycled off for 20 minutes on coldest days, 1-4 hours when warmer.

Comments

  • Zman
    Zman Member Posts: 7,610
    The first thing you need to determine is whether the boiler is cycling off the pressuretrol or the t-stat. If you jumper the t-stat you will know. What model is the t-stat?
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • JosephKenski
    JosephKenski Member Posts: 2
    The boiler is cycling off the tstat. It's a Honeywell CT 30 series. Over the last week the cycling has stretched out to 3-4 minutes on and 10-12 minutes off.
  • ImYoungxD
    ImYoungxD Member Posts: 130
    Steam should be on 1.2 anticipator
  • HVACNUT
    HVACNUT Member Posts: 6,220
    Check and clean the pig tail.