@MichelleLe1,
The pressuretrol is set way too high. This will also cause numerous problems.
Turn the adjustment on top until the right side bar aligns with 2 psi.
Do the side marked "main", not the "differential" side.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
That translates to 50,520 btus X 1.33 pickup factor = 67,192 btus. The boilers net rating is 89,000 btus which would mean it's a little over-sized, but that might be the smallest steam boiler that Crown offers (not sure). The burner MAY be able to be down fired some (not sure of that either).MichelleLe1 said:Here you go Bob.
I believe I have a total of 210.5 sq ft of radiation.
How many sq. ft. is your house?
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
-
@Ironman they actually have 2 sizes smaller in that series, but it looks like it’s done in the burner as they are all 3 section boilers. Give that it should be able to be downfired to a closer rating to her system.
They make factory piping kits for those boilers, I wonder if the factory would be willing to help out in our possible endeavor?1 -
I think the boiler can be down fired since it's the same 3 section block as the two smaller sizes in that line. You'll lose a little domestic hot water production, but not much.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
@KC_Jones,KC_Jones said:@Ironman they actually have 2 sizes smaller in that series, but it looks like it’s done in the burner as they are all 3 section boilers. Give that it should be able to be downfired to a closer rating to her system.
They make factory piping kits for those boilers, I wonder if the factory would be willing to help out in our possible endeavor?
I guess we were thinking the same thing at the same time.
Getting the piping kit would be very helpful.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Would a double riser drop header act as a main for all the runouts to connect to.
And is it feasible to drip each counterflow runout, or maybe just the longest ones.
The only venting would be at each radiator, does adding an air vent to the valve end of the rads vent the runout riser?
I tried that on a long run connected somewhat like this and it only vented at the end of the cycle. FWIW
And do you have an extra zero in you house size?0 -
I found this for the boiler piping kit:
Seems everything needed is listed right there
http://www.velocityboilerworks.com/documents/Kingston-Near-Boiler-Piping-Kit.pdf
Peter Owens
SteamIQ1 -
Oops! Yes. 1,530 sq ft 😲0
-
Well, that's a little over 33 btus per sq. ft. Sounds about right for an old house with steam. You probably have a lower heat loss per sq. ft. now if the envelope has been tightened up.MichelleLe1 said:Oops! Yes. 1,530 sq ft 😲
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
anyone mentioned turning the pressure down?
0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 65 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements