Is steam theory like water

Snowmelt
Snowmelt Member Posts: 1,425
I’m only asking, are you going to affect the final result if you take a three inch pipe and cut it to two inch.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,856
    More or less... doesn't really mind contractions. But doesn't care for expansions.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • JUGHNE
    JUGHNE Member Posts: 11,276
    I think it is all dependent on pressure drop.
    But for steam you have maybe 2 psi to deal with, with water we are talking 50-60 psi. You could lose some at that pressure and not notice it.
    But to me with steam that much drop because of that much 2" pipe seems like it would be noticed in performance. Just a WAG on my part.
  • Snowmelt
    Snowmelt Member Posts: 1,425
    Also what the hell is the second pic it looks like some sort of zone valve for steam?
  • Jamie Hall
    Jamie Hall Member Posts: 24,856
    Snowmelt said:

    Also what the hell is the second pic it looks like some sort of zone valve for steam?

    Probably is. Some systems did have powered zone valves off thermostats. They work. Sort of. If they are full port. Otherwise they are just plain trouble.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Snowmelt
    Snowmelt Member Posts: 1,425
    The art school did have 2 thermostat, one doing the gym other doing some of the rooms.
  • Tinman
    Tinman Member Posts: 2,808
    I see zone valves on large steam systems quite regularly now, mostly in very old churches and multi-family buildings.
    Steve Minnich
  • JUGHNE
    JUGHNE Member Posts: 11,276
    On the piping with the zone valves, is the condensate return pumped?
  • Snowmelt
    Snowmelt Member Posts: 1,425
    One zone is just for the gym, other is for about 8 rooms. That might explain the 280,000 btu. 140,000 for the gym 140,000 for the rest of the place. There is 2 zone valves so the answer would be yes, one of the zone valves is for the gym and is using a condensation pump.


  • Snowmelt
    Snowmelt Member Posts: 1,425
    The top pic is a 2 inch zone valve the bottom pic is a 3 inch zone valve. It appears some one replaced the three inch pipe with two inch copper and stuck a 2 inch zone valve there.
  • ChrisJ
    ChrisJ Member Posts: 16,315
    > @Jamie Hall said:
    > More or less... doesn't really mind contractions. But doesn't care for expansions.

    Why not? A radiator is a huge expansion.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Jamie Hall
    Jamie Hall Member Posts: 24,856
    ChrisJ said:

    > @Jamie Hall said:

    > More or less... doesn't really mind contractions. But doesn't care for expansions.



    Why not? A radiator is a huge expansion.

    And the steam does exactly what saturated steam does when it expands. It condenses. Thing is, that's great in a radiator -- but not in a steam main. Saturated steam is funny stuff...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Snowmelt
    Snowmelt Member Posts: 1,425
    JAmie now I’m confused, if pipes are bigger 3 inch instead of 2 inch it will condense. I thought smaller pipe will condense or have more velocity, or both. Let’s use this for example 280,000 btu in a 2 pipe vs 3 inch pipe.
  • ChrisJ
    ChrisJ Member Posts: 16,315
    It condenses because it's cooled by the radiator. As it expands the pressure drops which if anything keeps it a vapor longer.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Jamie Hall
    Jamie Hall Member Posts: 24,856
    Oh dear. I hate entropy. I hate enthalpy. I hate saturated steam.

    The problem, of course, is that saturated steam is a long long way from an ideal gas.

    OK. Let's start with the contraction. What will happen at a contraction is the steam will compress. The velocity will increase slightly and the pressure will drop slightly -- but the temperature will increase slightly. Now, however, if we encounter an expansion, the gas (steam) will try to expand. In doing so, the temperature will drop, When the temperature drops, if the steam is saturated -- that is, in equilibrium between liquid and vapour phases -- it will condense. Not all of it. But some (depends on the expansion ratio). Now in a radiator, the remaining steam condenses on the cool surfaces of the radiator -- which is just what we want it to do. In a steam main, though, it will condense onto the walls of the pipe. Which we don't want it to do.

    In extreme cases the result can be that practically no steam makes it past the expansion, which can really be tiresome.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England