As the old saying goes ”cant fix stupid”
Dave0176
Member Posts: 1,178
Got a call today for a heating issue, the HO had previously posted on here and you guys recommended me, thanks.
Anyway what I found was laughable as usual, an emensly sized boiler compared to the connected radiation. They installed a Williamson GSA 250,000 or a rebadged Weil-McLain EG65. After measuring radiation I came up 432 sq ft steam compared to the boilers rated net output of 654 sans the pickup factor. The funny thing is they removed a brand new Williamson GSA 150,000 (Weil-McLain EG45) because the HO when buying the house had done a complete rip out of everything and added radiators and they told him it would be way too small. Also they tried to mimic the B&J big mouths vents by using Watts steam traps which I told him to replace.
At this point I’m going to add a two stage gas valve and if that tames things a bit we will repipe it properly.
Anyway what I found was laughable as usual, an emensly sized boiler compared to the connected radiation. They installed a Williamson GSA 250,000 or a rebadged Weil-McLain EG65. After measuring radiation I came up 432 sq ft steam compared to the boilers rated net output of 654 sans the pickup factor. The funny thing is they removed a brand new Williamson GSA 150,000 (Weil-McLain EG45) because the HO when buying the house had done a complete rip out of everything and added radiators and they told him it would be way too small. Also they tried to mimic the B&J big mouths vents by using Watts steam traps which I told him to replace.
At this point I’m going to add a two stage gas valve and if that tames things a bit we will repipe it properly.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
1
Comments
-
For my clarification, the person who is hiring you is the one who picked this oversized boiler?0
-
Pipe it straight across with no swing joints. I don't get it. Fighting to get that connected and all you save are 2 elbows and then puts the system supplies between the boiler supplies. Don't know about the header size0
-
No,,, his plumbers recommend and installed this. He gets heat, however it comes along with the anvil chorus.KC_Jones said:For my clarification, the person who is hiring you is the one who picked this oversized boiler?
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
The header is sized right 3”, but that’s where it ends, however the boiler is 230 EDR oversized lol.EBEBRATT-Ed said:Pipe it straight across with no swing joints. I don't get it. Fighting to get that connected and all you save are 2 elbows and then puts the system supplies between the boiler supplies. Don't know about the header size
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
The anvil chorus is in part caused by the calliope the contractor installed. I don't suppose the installer did anything silly like skimming the new boiler?
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Dave,
Like you and most on this site, we see this type of near boiler piping almost daily. We're not perfect either, but you'd think they would at least look at the install manual one time! I'd be willing to bet that we see boilers piped this way more often than the correct way (steam and condensate flowing in the same direction).
With regard to sizing, also a common problem, I guess others are too busy to spend fifteen minutes measuring standing radiation. The good news is we only see oversizing about a quarter of the time.0 -
I think you can fix stupid.
Open your eyes. Open your ears. Close your mouth. Open a book.
Indifference and laziness would be much harder to change.Steve Minnich0 -
I agree, stupid has a fighting chance under the right conditions. Ignorance, indifference and laziness - not so much.0
-
Stephen Minnich said:
I think you can fix stupid.
Open your eyes. Open your ears. Close your mouth. Open a book.
Indifference and laziness would be much harder to change.
Keyword Laziness,,,,,,,, Find and see it all the time.......Dan_NJ said:I agree, stupid has a fighting chance under the right conditions. Ignorance, indifference and laziness - not so much.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements