Vents to regulate temp
JodiMe
Member Posts: 74
Hey all. My daughter’s room is the furthest from the boiler, so the only time it really ever heats well is when we are pumping the early morning heat or in the early evening when we arrive home for the day. It ranges from 67-73...67 when the heat is just maintaining temp (we keep it set to 69-70) and 73 in the morning/evening push. I’ve currently got a Maid-o-mist angled vent on, size 5. Is there a way to regulate this at all to stay closer to the temp we have the main thermostat set at?
0
Comments
-
What is your main venting like? This sounds like a main venting issue. All radiators should be getting steam to the inlet valve at around the same time, in the whole house.
It all starts with the main venting in the basement.2 -
-
Our main venting was just replaced a couple years back and it made a big difference with even heating, generally. I thought it was pretty even until we had a baby and ended up with a monitor that also track temperature. Would a photo help? I don't really have details otherwise.0
-
Pictures of your main venting and knowing how long and what diameter the mains are will help us determine if you have enough venting. If you know the actual brand and model of the vents that would be a big help too. Many times we can figure from pictures, but actual data is always better.0
-
Got it. I'll try and gather info/pics tonight. Thanks!0
-
I second taking a look at the main venting. Until I replaced the main vents and then balanced the radiator vents, "room temp" across the house would vary by up to 5-7 degrees. After balancing the venting, "room temp" is the same across the house within .5 of a degree. Properly sized main venting makes all the difference.0
-
I did a little experiment and put another thermometer in that room, but at living level (the monitor is mounted close to the ceiling) and it seems that the high temp reading is because of the location of the monitor. The other thermometer read exactly where it’s supposed to be when heating.
I think we have a bit of an insulation issue, however, as it seems to get cold quickly.
Thanks for the help, everyone.
0 -
If you replace failed main vents with inadequately sized vents, there is still room for improvement.
Let us see your main vents.--NBC0 -
It’s really difficult to get a photo of as it’s up inside the wall, but here it is. As I mentioned before it was replaced about 2 years ago. If I recall they maybe mentioned it’s a bit too small for the house but that’s all that would fit. Don’t quote me on that 100% though... Also included a pic of the boiler spec label. We’ve got 2 floors, 1375 total sq ft, 4 convection radiators on the first floor, 1 convection in the upstairs bathroom, three bedrooms that each have cast iron radiators.0
-
How long and what diameter mains do you have? That is a Gorton #1 in your picture. Unless your main is about 10 ft. long and 2 inches in diameter, that vent is too small.0
-
I would say the venting needs improvement. Those look like Gorton #1, and probably only capable of servicing 10 feet of 2 inch line.
I would try Big Mouth vents alongside the present ones.—NBC0 -
I don’t know what all of that means! Ha. I’m pretty novice. But we will have someone come in and take a look at it. Generallly, our heating is pretty even but yes, could use some improvement. Thanks!0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements