Boiler stops running after a few hours
kiemside
Member Posts: 10
in Gas Heating
It is a gas steam boiler with a wired-in thermostat.
Everyday, it always runs first time I turn it on. But it stops running after about 2 hours.
When it runs, I use a multimeter to check and find voltage at the thermostat and between terminals C and R and between terminals C and Y at the transformer.
When it stops running, there is no voltage at the thermostat and also nothing between terminals C and Y. However, there is still voltage between terminals C and R at the transformer.
The vent damper is on always on the "open" mode.
Does anyone know what is going on?
Everyday, it always runs first time I turn it on. But it stops running after about 2 hours.
When it runs, I use a multimeter to check and find voltage at the thermostat and between terminals C and R and between terminals C and Y at the transformer.
When it stops running, there is no voltage at the thermostat and also nothing between terminals C and Y. However, there is still voltage between terminals C and R at the transformer.
The vent damper is on always on the "open" mode.
Does anyone know what is going on?
0
Comments
-
Does your pressure switch shut it off?
If so it should start again if the T-stat is still calling for heat.0 -
Or any one of several other safeties -- like a low water cutoff?JUGHNE said:Does your pressure switch shut it off?
If so it should start again if the T-stat is still calling for heat.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I found the culprit. It was the pressuretrol and its pigtail pipe, which were clogged. I open them up and cleaned them. Put them back together and the boiler was running all night.
I guess because of the deposit inside the pressuretrol and the pigtail pipe, the pressure never got back down to the cut-in pressure. As the result, the boiler doesn't turn back on after running for a few hours.0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 892 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements