New return duct sizing
jr365
Member Posts: 2
I have a 1970's 1100 sq ft ranch on a slab. The return duct is in the attic and is in need of replacement. Instead of putting a new return duct back into the attic, I would like to move it into the conditioned space.
There is only one large return vent, located in the hallway between the bedrooms. It would be about a 30ft. run of duct from the furnace, with three 90 deg elbows. An online ductalator calculated the diameter of a round duct at around 14.5" for my 2 ton system.
The best size for where I want to put the duct would be a 14" max diameter. Would a 14" duct work or would I need to move up to the 16"? Thank you for any help.
For residential return duct you should really consider velocity versus friction. The 16 inch will keep you under 600 fpm and may be a better choice.hvacfreak
Mechanical Enthusiast
Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV'sEasyio FG20 Controller
-1 -
Thank you all for your replies.
The plan was to run it in the house along the corner of the wall and ceiling. Basically following the same path as the existing return, but inside the home.
I wanted to go with spiral duct, to avoid having to frame out and drywall another type. I don't mind the look of an exposed duct, and it would avoid a lot more work and expense. Biggest reason to keep it no bigger than 14" is so it fits in the space above the doors. Any larger and it would overlap the top of the doors.
Would making the vent opening larger, help make up the difference in the duct size difference, or maybe a larger air filter? Or both?
Can I ask why you want to remove the return from the attic?
If you run exposed spiral duct, how does the intake grill configure? I assume its going round to square/rectangle at some point.0
