Smith GB100W boiler problem/question
astoria2013
Member Posts: 16
in Gas Heating
I have a new customer that has 3 of these boilers that has to at least 2 times a year change rollout Switches. His chimney is 10 inches which I suspected was the Problem, but upon further inspection I found this. See pic. Has anyone ever seen anything like this before? All 3 boilers have it. Just a plate covering 3/4 of flue right before vent damper. Boilers are 50,000 btu. Nothing in manuals I have found have any mention of this plate which seems to be part of boiler. Thanks in advance.
0
Comments
-
If it's factory installed, I wouldn't worry about it.
You obviously have a chimney issue. 10" is way too large for a 50k btu appliance or even for three of them if they're common vented. What's the chimney height? Is it a masonary chimney on an outside wall?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
-
That certainly is a fusible link rollout switch when typically there is a spill switch in that location.
Check the key on the wiring diagram to see if that's the correct part.0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 891 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements