Storage tank vs boiler
kevsul1
kevsul1 Member Posts: 28
What is the benefit of having a wall hung boiler that is piped to a storage tank vs one that does it internal in the boiler itself
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,584
    I assume you mean a combi vs an indirect? You can generally size the boiler to the heat loss with an indirect. A combi needs a larger input to handle instantaneous DHW.
    kcopp
    EBEBRATT-Ed Member Posts: 19,616
    a more accurate boiler sizing. less short cycling, less boiler ware & tear. more dhw
  • NY_Rob
    NY_Rob Member Posts: 1,370
    Wall hung is less expensive, simpler (less parts to break) and easier to service vs. combi.
  • Zman
    Zman Member Posts: 7,611
    Wall hung boilers usually heat domestic water via indirect water heater (IE tank with coil inside).
    I think the other option you are thinking of is a combi boiler?
    With the indirect, you can size the boiler to the heating load and use the storage buffer to get you through periods of higher DHW usage.