Help... Three zone home
udhoop
Member Posts: 4
I need some help/ advice prior to discussing this issue with our contractor again. We have a new home with radiant floor heat. We have three zones with a thermostat for each. (Basement, main floor, upstairs)Each level has its own manifold as well which runs three to four loops. It is heated by a Lochinvar Noble combi gas boiler. When having this installed the idea was that each zone would work independently based on its own thermostat. However, I have discovered that when one zone calls for heat we have heat going to all three manifolds/zones. There is a pump for each zone. So as an example, if I go upstairs and bump up my thermostat so that zone calls for heat then go downstairs I will see that our boiler has kicked on and I can feel the pump for the upstairs zone working. So that is good. However, if I go around to the other manifolds each has hot water going through them. Like too hot too touch water. While their pumps don't seem to he actively working its as if they are open and the whole system is receiving heat. Our contractor says they receive "residual" heat from "some" water passing through. However, a friend of ours who also has this same design and setup says this should not be happening. When he has a zone call for heat only that zone is receiving heat and his other manifolds are cool to the touch. The example I gave happens regardless of which zone I bump up. We are in Nothern MI so its not a big deal with regards to the main floor and upper level but with our basement receiving heat every time it is a sauna! Code required us to put down r-15 foamboard which we stapled too and then the whole basement has r-10 foamboard around the exterior so it keeps the heat in extremely well. Any ideas on why all three zones are receiving heat when only one zone calls for it?
0
Comments
-
-
The pump in the upper left is for our upstairs. The pump just to the right up that is for the main floor and the pump to the far right is for the basement with its manifold directly below it.0
-
There are no check valves on the return lines of the zones.
when the boiler pump circulates it will increase pressure and push water into each zone even if the zone pumps are not calling.
some circ pumps have built in check valves. It appears that yours do not.
Start with that. it is not a huge modification to do.
-1 -
-
-
Does that green sticker say 'Final Inspection'?0
-
Can you take a picture of the boiler with the cover off? I believe there is a circulator inside.
Aside from the pex and crimp fittings being just plain ugly, it is piped completely wrong.
I think you need to find a contractor who can read to repipe it, preferably in copper."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements